Air transfer through soffits

user-6514939 | Posted in General Questions on

Hi Martin….I am building in zone 5 and have chosen to spray the roof deck with closed foam backed with open cel. There will be no air coming in through the soffits since the foam fills the roof joist cavity above the plate on the outside walls. My question is regarding the roof joist tails beyond the exterior walls. My intention was to close those soffits with cedar without any venting considering there will be no way for air to get out if I allowed it to get in. Is this an acceptable practice? or should I install a continuous vent on the underside as usual….assuming air will move in/out from the underside?

I fear after seasonal temperature changes that the tails could warp if they cant breath.

Thanks

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Consor,
    Either way is fine. If you have a ventilated soffit, it can stay. If the soffit is unventilated, that is fine, too.