Air sealing at top plate
![](https://secure.gravatar.com/avatar/b2e4a094adc6bea7d52f2beeb965a79b?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
I am owner-builder on an extensive remodel where the entire above-grade structure above the floor joists is being replaced. After extensive planning and research prior to start of construction, I was off to a good start on air-sealing details with EPDM gaskets under the sill plates, and acoustical sealant on-hand for sealing sheathing to the sill and top plates. However as I feared, at some point the framers forgot to apply the acoustical sealant on some large sections of wall, and now I’m uncertain exactly how to air-seal at the top and bottom of the walls.
I am considering some sort of self-adhered flashing at the bottom to seal the sheathing to the foundation which I can seal the WRB to. I can’t think of any way however to effectively seal the top of the wall and make it continuous from the sheathing to the air-tight drywall in the ceiling. I think switching to an unvented roof and spray foam might be a solution, but that would really strain the budget and therefore may not be an option. Is there another way to make the air-barrier continuous with the already installed sheathing? Would caulking or consumer spray foam from the inside provide enough of an air-seal? Am I overthinking this?
Any advice would be greatly appreciated!
-Chad
Chad,
Q. "I can’t think of any way however to effectively seal the top of the wall and make it continuous from the sheathing to the air-tight drywall in the ceiling."
A. You should read this article: "A Practical Air-Sealing Sequence."
Thanks for the reply Martin. The link you referred me to is actually the method that I was aiming to follow, however the opportunity to seal the sheathing to the top plate was missed (unless I insist that the framers pull off the top row of sheathing and re-apply with adhesive).
Any thoughts on how to achieve a reasonable seal after the fact?
When using a plywood cap plate, is a SDWC Truss screw used in place of a hurricane clip?
Mark,
You can use the screws, or mount the truss-clip on the exterior.
Green,
Q. "The opportunity to seal the sheathing to the top plate was missed (unless I insist that the framers pull off the top row of sheathing and re-apply with adhesive). Any thoughts on how to achieve a reasonable seal after the fact?"
A. Tape. For more information, see "Return to the Backyard Tape Test."
Martin, maybe I'm being obtuse but I don't understand how to carry the seal through from WRB/sheathing to the interior ceiling drywall using tape. I'm not even sure that caulking around every single stud bay and between top plates would provide a complete seal. Even spray foam sealing all around the top plates from the attic seems like it would still leak between studs and sheathing. At this point I think I'm willing to settle for just a "good enough" seal, but I'm still not grasping what that is yet.
Green,
Q. "I don't understand how to carry the seal through from WRB/sheathing to the interior ceiling drywall using tape."
A. You should re-read the Fine Homebuilding article I linked to. The key to the suggested method is the 3/4-inch plywood cap that cantilevers inward. The wide plywood cap goes on top of the top plate of the wall. Read the article carefully and study the detail drawing.