Air leakage from pan drain

Remodelpro | Posted in Energy Efficiency and Durability on

We just completed a blower door test on a finished home and I was surprised how much air was leaking out of the 1″ water heater pan drain. Is there a code compliant way to prevent this air leakage and still allow the drain to function if the water heater leaks?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Anthony,
    (1) You can install a trap in the drain line. Pour some mineral oil in the trap to create an air seal. (Mineral oil evaporates more slowly than water.)

    (2) Get a condensate pump and route the drain line to a nearby laundry sink. (This works if the sink drain has a trap and if the sink is used regularly enough to keep the trap from evaporating.)

  2. Expert Member
    MALCOLM TAYLOR | | #2

    Anthony,

    Are you sure the trap just hadn't been filled? Our code mandates traps on all interior drains. As Martin said, they can dry out, but mineral oil stops that.

  3. Remodelpro | | #3

    Thanks Martin and Malcom,

    Typically overflow pan drains must be routed to the exterior of the building (Daylight) and most inspectors do not allow them to be trapped.. Any other suggestions?

  4. Expert Member
    MALCOLM TAYLOR | | #4

    Anthony,

    There is manufacturer that makes back-flow valve drains that also are very air-tight. Unfortunately I can't remember the name - but I'm pretty sure it has come up here on GBA. Perhaps another poster can remember it.

    Edit: The reason I said A manufacturer is that a lot of the back-flow values work by closing the drain with a float when water comes up from below. The one I'm thinking of works similarly to an air admittance valve, using a spring. So it is always closed unless there is water from above.

  5. Expert Member
    MALCOLM TAYLOR | | #5

    Another option to get around the inspector's allergy to traps is to terminate the pan-drain near a floor drain (which presumably has a trap). This is allowed in the 2015 IPC.

  6. Remodelpro | | #6

    Thanks Malcolm,

    I believe that this is the back flow valve you are referring to.
    https://www.rectorseal.com/waterless-kits/
    I believe that this solution will make everyone happy.

  7. GBA Editor
    Martin Holladay | | #7

    Anthony,
    Thanks for the link.

  8. Expert Member
    MALCOLM TAYLOR | | #8

    Anthony,
    Yes, that's the one. These type of problems are annoying to deal with. When each jurisdiction has different standards, you realize how arbitrary they are.