During a project review with our architect (has his CPHT/CPHD) he mentioned the possibility of using an aerogel infused spray on coating called “Aerolon” from a firm named Tnemec (www.tnemec.com) as a possible solution to mitigate any potential thermal bridging in our project not easily solvable by more traditional methods. I’ve been a big fan of Aerogel in its various forms for many years but was not aware it was now available in a spray on coating. Checking with the GBA community on anyone’s experience or background with this or similar type coatings.
"Insulating paint" sent my eyebrows to the sky, because there have been some very scammy products marketed as insulating paint, claiming absurd R-values (there are some articles calling them out on this site). However, I looked this stuff up and I don't think it's a scam -- but construction is not really a good application for it either. The spec sheet is here: https://tnemec.com/products/series-971-aerolon-acrylic/ -- note that the thermal resistance is quoted at R-4.1 at one inch, which is a physically reasonable number comparable with things like EPS foam -- but as a "spray-applied coating" they're recommending application at a rate of 50 mils (0.05") thickness per coat, so it'd take a while to get any significant R-value built up!
The intended application for this stuff is coating metal pieces in industrial / building plant applications -- think big pipes carrying chilled or hot process fluids. In that application, the comparison is between steel, with a thermal conductivity of 45W/m*K and this stuff, with a thermal conductivity of 0.0356W/m*K -- the claim is that even a thin coating reduces the thermal conductivity enough to improve safety (ie the time it takes to burn someone when accidentally touching a hot pipe) and reduce condensation on cold pipes, while also protecting pipes from corrosion.
I'm not in a position to evaluate whether these claims are valid or not, but they're at least physically believable -- but the fact remains that to get any substantial R-value out of this coating, you'd need to build it up to a thickness comparable to standard insulation materials -- and it'd definitely be easier to use something else in standard construction, unless you have a bunch of 12" chilled water lines running through your house. I'm betting your architect saw this specified on a commercial project, or perhaps saw a seminar on it as part of continuing education, and thought it sounded cool -- but I can't see any application for it in residential construction that couldn't be better solved with another material.
Those numbers would give them a very tiny by over R 0.2 in that 0.05" thick coating. Not nothing, but not enough to really do anything in terms of reducing thermal bridging, either. A layer of 1/2" polyiso would be R3, fifeteen times better.
I can understand their interest in safety in industrial settings. The usual things I work with are chilled water lines, running around 40-45F or so, and those don't have much trouble with condensation. The hangers only contact the pipe through a relatively small contact area in the "saddles", and the rest of the line has a rigid fiberglass insulating wrap. It might be different with high pressure steam lines though, which can be up to 1,000F or more, a little extra protection might be really helpful.
I agree with Jonny. Tnemic is a legitimate company; they've been making high-quality metal coatings forever, but I don't see where this product would make sense on a construction site.
What's the detail that specifically wants a thermal break coating? I'm having a little trouble imagining a situation where a thermal break coating is the only solution.
Is it something where a structural thermal break product could be used? For example, rather than coating a metal structural element that passes through the envelope, perhaps a structural thermal break could be used to separate the interior and exterior portions. Here is an example of a structural thermal break product: https://www.armatherm.com/thermal-break-materials/armatherm-frr/