Adding return duct on second floor?

runner9 | Posted in Energy Efficiency and Durability on

We have a bungalow, built in 1954 that probably had a gravity furnace to start. It’s had an addition, so upstairs is now three bedrooms, a bathroom, 2 large closets. There are 5 forced air vents upstairs and no returns. You can feel the air rushing down the stairs to the first floor, where it mixes with the 1st floor air and then finds the three return ducts on the first floor.

I’m removing an unused chimney later this week and that will open up a space from almost the top of the stairs, on the side wall, all the way to the basement.

I’m trying to decide if adding a return vent there makes sense. A quick internet search says no, that as long as the air has a way down it’s fine and that more supply is more effective. I would have thought that a straight path for that cold air to the furnace without cooling the first floor first would be preferred.

Opinions and reasoning welcome.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Jeremy,
    Ideally, every room in the house -- especially bedrooms -- that has a supply air register also needs a return air pathway from the room back to the furnace. Installing proper return air grilles in your upstairs rooms makes a lot of sense.

    Here is a link to an article with more information on this issue: Return-Air Problems.