Achieving secondary air barrier in roof assembly with untaped sheathing

dschreiber41 | Posted in General Questions on

1920’s Baltimore masonry row home, stripped to the shell, floor decks and roof installed.  “Cockloft” roof  framing.  Low sloped roof has modified bitumen over only 2 inches of polyiso and 3/4 ply sheathing.  Roof had been replaced recently, so we’re stuck with that assembly.  

In an ideal world, I use that term with hesitation, we’d have more polyiso and the sheathing seams would have been taped prior to insulation install and tied into the parge coat (and/or our liquid applied membrane – design stages at the moment).

Wall assembly is intello plus over 2×6 framing, held off the masonry (parged), cavities filled with dense pack cellulose (we can argue the merits/pitfalls of this assembly elsewhere), service cavity over the intello, at the moment, cavity will not be insulated.  

I’m happy to provide more details, but given our original plan was an unvented roof assembly, with dense pack gutex (we have enough room at the lowest portion between the roof deck and ceiling framing to get r-49, but holding it below the sheathing about 3 inches) and those sheathing seams aren’t taped (to form our secondary air barrier), should we be modifying the aspects of the roof/ceiling assembly that we have control over?  

ACH50 goal is 1.0.  Spray foam is not an option though I’d be happy to hear how that could potentially be implemented for future projects.  I’m very much aware that there are many ways to do this, and that depending on your constitution, which party line you’re toeing, some are certainly more preferable than others.  

I imagine I haven’t provided nearly enough detail, so please let me know what other information would be helpful.  Thanks very much.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Akos | | #1

    First thing is in zone 4 you need R15 above the deck for an unvented R49 roof. Your 2" polyiso is close but not quite there. I would check what U factor your local code allows and comply based on that. If it is R38 or R42 equivalent, you a good with the 2" polyiso.

    More details about the ratios here:

    https://buildingscience.com/documents/building-science-insights-newsletters/bsi-100-hybrid-assemblies

    The fluffy insulation under the deck needs to be right up against the roof, you can't have a gap. A gap there is a code violation plus it creates this in-between space that is neither indoors or outdoors which can create condensation and mold issues. Make sure there is no vapor barrier under the fluffy as the roof cavity needs to dry towards the interior.

    With a torch down roof, your air barrier is the actual membrane. You can tie your wall air barrier to it on the outside. Do your best to detail your ceiling drywall as the secondary air barrier (ie drywall gasket at the perimeter and any interior partition walls).

    As for your walls I would read through this. The wall you are building can sometimes work but can also fail.

    https://buildingscience.com/documents/building-science-insights-newsletters/bsi-105-avoiding-mass-failures

    1. dschreiber41 | | #2

      Many thanks