Acca outdoor design temperatures trust

buildzilla | Posted in General Questions on

What should I say to an HVAC guy that says they don’t trust acca outdoor design temps in cz-6 and wants to substitute -11 for -22 which is why the equipment will b oversized from a manual-j calculation?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. b_coplin | | #1

    "Can you show me bin hour data--or any empirical evidence--to support your position?''
    I suspect your contractor has chosen the lowest temperature your area routinely sees--but this is only for an hour or two a year.

    If you are in a mountainous area, it's possible that your local conditions are different than the nearest weather station; I would still press for measurements.

  2. BirchwoodBill | | #2

    Run a report for temperature from the the manual and then one for the lowest temperature. Ask the contractor if that changes the equipment recommendation or the size of the ductwork.

  3. Expert Member
    Michael Maines | | #3

    Considering that just a few months ago we had -20°F in CZ6 (Maine), I can see why they may want to be conservative. If you have a poorly insulated, drafty home, equipment may not be able to keep up. But one of many advantages of a well-insulated, airtight home is that it can more easily ride out those brief extra-cold spells.

    1. buildzilla | | #4

      yeah, this would be for a new high performance build, so i'm thinking to stay the course.

      i told the people that i trust the ashrae data, and they were like ok,
      just don't come crying to us if your house is cold (i'm paraphrasing) :)

      i punched some diff design temps into cool-max and for this case, it was about 1000 btu for every 1 degree F (eg the diff between -10 and -20 was like 10k btu)...

      1. Expert Member
        Michael Maines | | #5

        Few HVAC contractors have much experience with high-performance homes, and their worst nightmare is a client calling to say they aren't warm enough.