5.5 Inch Flue Liner on a 6 Inch Collar

mrmojorock | Posted in General Questions on

Hi –

As many people have asked this question – I understand that undersizing flues greatly impact the performance of a stove. I saw a similar question on here from a member about undersizing from 7″ down to 5″ – which is substantial.

My question, however, is if an undersize from the 6″ recommended to a 5.5″ liner would see a drastic impact. We’re working with a 25′ chimney stack and a few bends which have prohibited the 6″ pipe from being installed.

For reference – I’m installing the liner to a Jotul Oslo wood burning stove using a heavy-duty flex liner.

Any thoughts or advice is very much appreciated.

Thanks!

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Michael Maines | | #1

    You're looking at a 16% reduction in capacity as opposed to a 50% reduction to go from 7" to 5". Assuming the bends are minor, you have decent height so I bet it will work ok.