R-3.33 vs. R-4.16 window R-value (or U-0.30 vs. U-0.24 U-value)

RussMill | Posted in Energy Efficiency and Durability on

Without using modeling software can someone give me an anolgy or example of windows with a .83 R / .06 U Value DIFFERENCE…??
While location, size and overhang all change window performance any rough ideas or examples for me?

In an r-40 wall i wouldnt worry about an R1 difference but SHOULD WE ON WINDOWS, care about that difference. Climate zone 4 on edge of 5!
THANKS AS ALWAYS!

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Aedi | | #1

    I'd say the U-0.30 windows are about 25% better :p

    In all seriousness though, it is better to think of thermal resistance in terms of proportional difference than absolute difference. The difference between an R5 and an R10 wall is much more noticeable than the difference between an R50 and an R55 wall. Since a lot of a wall's heat is lost through its weakest points, that extra 25% could make a big difference.

    But it is impossible to answer your question without extra information. If you don't have many windows, then it won't make much of a difference and you should go with whatever is cheaper; conversely, having many windows would would weigh heavily for the higher U-factor. Plus if the windows have different glazings and emissivity values, it changes the whole comparison.

    Calculating the whole-wall R value with the two different windows would be a good start to know how big of a difference it makes.

    1. RussMill | | #4

      Thanks very helpful.

  2. Expert Member
    Dana Dorsett | | #2

    >"In an r-40 wall i wouldnt worry about an R1 difference but SHOULD WE ON WINDOWS, care about that difference. Climate zone 4 on edge of 5!"

    An R40 (whole wall) wall has U-factor of 1/40= 0.025 BTU/hr per square foot per degree F temperature difference.

    An R41 (whole wall) wall has U factor of 1/41= 0.0244 BTU/hr per square foot per degree F temperature difference.

    So a change of R1 only results in a 0.025- 0.0244= 0.0006 BTU/hr per degree F difference (big whoop, right?)

    The difference between U0.30 - U0.24= 0.06 BTU/hr per degree F difference.

    The effect of an R1 improvement in windows is a 100 x bigger than an R1 improvement in an R40 wall.

    That means an R1 improvement on just ONE ten square foot window has a bigger impact than an R1 improvement on all the walls and attic combined.

    But you shouldn't "...worry about..." it- you should do the math.

    In a zone 4/5 location it's definitely worth upgrading to an R0.25-ish or better window, which isn't a hugely expensive upgrade compared to going from a code-min U0.060 wall assembly upgraded to a U0.025-ish wall assembly. Just about any argon filled double-low E double pane gets you there at a price point well below triple panes.

    1. RussMill | | #3

      Thanks Dana, for putting in perspective.

  3. Peter Yost | | #5

    It's worth noting that higher performance windows most often lead to increased thermal comfort as well as greater energy efficiency.

    A quick and easy way to compare window performance is the Efficient Window Collaborative window selection tool: https://www.efficientwindows.org/new_selection1.php

    Peter