I have a vented attic in zone 4c. Any other relevant info I may miss that’s needed let me know.
I have a single story home I’m working on, and it would be very easy to run both fans into the same 6” smooth exhaust vent pipe. The first runs straight out of the house with one swooping 45° In total in about 12’ all 6” smooth.
im wondering if I can tie in a second 6” smooth to that existing system. It would run about 20-30’ total, with maybe 4 elbows. Is this ever OK? Are there length requirements elbow limits etc when trying to split, or just never a good idea.
Both fans have 80 or 110 cfm.
thanks.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Nope, don't do it. You will backdraft smells from one bathroom into another and they will interfere with each others operation when they are both on. What you can do is use an inline fan to draw air from both bathrooms. That is, you can join your intakes into one but you can't join your exhausts.
hmmm. I did something similar but my join was at the roof deck with a y connector. the inspector and I talked about it and he said it would be fine. Note that my vent where it meets the roof deck is about 4 feet above each fan. The y connector is right up to the roof deck as well.
We tested this with one on and one off and both on. No impact at all. Both fans are 80 cfm running into a 4" insulated flex up to a 4" exit vent. both vents held a napkin with one or both on.
That said, our risk is low as on vent if for in inboard 1/2 bath. So, virtually no use.