    I need some help on insulation
    I built my house 4 years ago and used fiberglass blown-in insulation in the attic. I went up and found that the fiberglass has settled down about 4 in., so i am going to get more insulation to blow in. But do I use more fiberglass or do I get some cellulose and blow it on top of the old fiberglass ?
    Either one
    Ryan,
    1. Either product will work. If it were my own house, I'd choose cellulose.
    2. Remember, more insulation is better than less. As long as you're installing more insulation, you might as well install as much as you can afford.
  3. Bryce | | #3
    ORNL Study
    Martin
    The article I have in my files from Home Energy, May/June 1992, discussing the ORNL tests, indicate that the R-value of the blown fiberglass began deteriorating at approximately 30 degrees F, due to convection currents within the product. I believe the University of Illinois arrived at similar information under testing they performed on blown fiberglass. From personal history, I can attest that homes with blown fiberglass have higher ACH under a blower door test and have higher energy consumption than similar homes with cellulose.
  4. GBA Editor
    Martin Holladay | | #4
    Response to Bryce
    Bryce,
    Thanks for your post. You bring up some important concerns. I discuss some of these issues, and more, in my recent Fine Homebuilding article, Blown Insulation for Attics: Fiberglass vs. Cellulose.
    Here are the links:
    http://www.finehomebuilding.com/how-to/articles/blown-insulation-for-attics-fiberglass-vs-cellulose.aspx?ac=fp
    http://www.finehomebuilding.com/PDF/Protected/021216059.pdf
  5. beichenlaub | | #5
    Vapor barrier
    I live in Northern Michigan. What about vapor barriers and cellulose in new home construction? I am building with a double wall 8-10" of cellulose.
  6. GBA Editor
    Martin Holladay | | #6
    Response to Charles Eichenlaub
    Charles,
    In your climate, most building codes require a vapor retarder, not a vapor barrier, on the inside of your wall. You should avoid the use of polyethylene. Vapor-retarder paint (over the drywall) will work fine.
    Of course, airtight construction techniques are much more important than whether or not you include a vapor retarder. Do your best to seal all air leakage points.
    Here is more information on vapor retarders:
    Vapor Retarders and Vapor Barriers
    Forget Vapor Diffusion — Stop the Air Leaks!
  7. jmfb_k7 | | #7
    I have seen mineral wool as a blown insulation option, and I wonder how it compares to fiberglass and cellulose. I know it is flame retardent, but does it settle? Can it be damp-sprayed like cellulose? Does it stop air movement as much as cellulose?
      RICHARD EVANS | | #8
      Jmbf,
      I'm no expert on it, but I've looked into before.
      American Rockwool Premium Plus is a brand that comes to mind. They recommend blowing in the mineral wool at 4# density which is similar to cellulose and 2X+ blown in fiberglass. I would guess that cellulose is still a bit less air permeable however. Not sure about settling.
      The product can be sprayed in but it isn't a wet spray so much as it is sprayed in with a binder (like JM Spyder). I'm going on memory here...
      Of course the big performance difference between mineral wool/fiberglass and cellulose is that mineral wool is hydrophobic and cellulose is hydroscopic. Cellulose keeps moisture away from your sheathing and studs. Mineral wool (like fiberglass) will not.