Unvented combustion appliances were added to the scope of ASHRAE’s residential ventilation and IAQ standard (standard 62.2) recently. The committee has begun their deliberations on the issue, and at ASHRAE’s winter meeting in Orlando last month, the unvented gas appliance industry folks attempted a defense of their products. Based on the results they presented and the reaction from most committee members, I’d say they failed.
Water vapor and carbon dioxide
The 62.2 committee opened their meeting on January 22 with a presentation on the results of a study paid for by the unvented gas appliance industry. They hired a toxicologist named Dr. Gary Whitmyre to do a modeling study to see how operating unvented gas appliances in a home can affect the relative humidity and carbon dioxide levels.
He may have looked at other combustion products as well, but I came in late and didn’t see all the slides. The water vapor and CO2 results, however, provided plenty of reason for caution.
The effect of unvented gas appliances on relative humidity (RH) in this modeling study was that the worst 10% of homes could have RH high enough to create significant moisture and mold problems. The worst 1% likely would be “mold disasters,” as one committee member put it.
The study also showed that unvented gas appliances would add about 2,000 parts per million (ppm) of carbon dioxide to the indoor air. Note that this is what is added to the existing CO2 level, not what the total would be. Current thinking is that indoor CO2 levels should be limited to 1,000 – 1,200 ppm, so if a home with unvented gas appliances is already at, say, 1,000 ppm, the occupants could easily be breathing 3,000 ppm while the unvented gas appliance is running. The result could be drowsiness and impaired cognitive function.
Committee discussion
The ASHRAE 62.2 committee raised a lot of questions about the study. The unvented gas appliance industry folks who sponsored the study certainly didn’t help their cause. One committee member said, “The result of yesterday’s presentation is that I’m more concerned about unvented appliances than I was before I got here.”
On Saturday, they also voted on a proposal to adopt the following language into the residential ventilation standard: “Unvented combustion appliances except for cooking appliances covered in Section 5.1 shall be prohibited.”
After discussing it, the vote was 7 in favor, 10 opposed, and 2 abstaining, so the motion failed. But it was close, and the only reason it didn’t pass is that some members felt that the committee hasn’t really seen enough data yet.
After more discussion on a different proposal, a committee member proposed that homes with unvented gas appliances have to supplement their ventilation rate by 1 cubic foot per minute (cfm) per 1,000 Btu/h of appliance capacity. That proposal was referred to a subcommittee so they can discuss whether that’s the right number or not, but there seems to be support for something like that.
In other words, the unvented gas appliance industry would be handing off the cost for venting to the builder, who would have to add more ventilation to the home. Of course, they could just switch to vented appliances.
The prevailing opinion in the broader community
The representatives of the unvented gas appliance industry like to be dramatic. During the discussion of the proposal to prohibit them, one said that if the motion passed they might as well not continue on with the research project they were discussing because “there won’t be an industry left when it’s done.”
Well, there will certainly be a gas appliance industry left. All those fireplaces will be vented, though, as they should be. The truth is that unvented combustion appliances don’t belong in homes. (Yes, a gas range and oven are technically unvented, but the 62.2 standard requires a ventilation hood be installed there.)
There’s good reason that unvented combustion appliances are banned in homes in Canada and California as well as by most green building programs. Even when they’re operating properly, the water vapor and CO2 added to the indoor air can create problems.
“No professional I know would recommend an unvented device,” said Robert Bean. I’m with him.
ventfree products
We at fireplace Creations have been tearing out ventfree fireplaces for years. There is a pile in front or our store that we removed in 2015 & replaced with directvent gas fireplaces & inserts. Its really hard to believe were still having to discuss this topic. All of us that have been in this industry for the last 20 years or more. Knows the truth. Ventfree fireplaces & logs are not good for our homes or families. The truth is Ventfree products are sold mosly on mis or no information. Then we have the problem of the turn over of homes. We get 100's of calls every year . Consumers complaining about there fireplace. We ask the Question is your fireplace vented or unvented. 90% have no clue. If they don't know what they have ,they sure don't know all the warnings and instructions on how to use the ventfree product. Its really sad our industry as allowed this nonsense to continue. Its sure no fair too all the consumers that are having to spend all the money to have there ventfree product replaced & many having to repaint there home because of soot . Not counting all the possible health related issues.