![](http://images.greenbuildingadvisor.com/app/uploads/2018/07/24210800/hvac-air-conditioner-condensing-unit-refrigeration-cycle-main-700x525.jpg)
Image Credit: Energy Vanguard
Image Credit: Energy Vanguard A diagram of the refrigeration cycle.
Image Credit: Energy Vanguard An evaporator coil for an air conditioner. This type is called an A coil.
Image Credit: Energy Vanguard A frozen refrigerant line at the condensing unit of an air conditioner.
Image Credit: Energy Vanguard A diagram of an expansion valve.
With the recent heat wave that set all kinds of records across the US, including an all-time high of 106° F here in Atlanta, air conditioning has become quite the topic of conversation. Why, just yesterday I overheard two little old ladies* on a park bench debating thermostatic expansion valves versus capillary tube metering devices — and almost coming to blows over it! Most people aren’t quite as informed as these air conditioning aficionados, though, so today would be a good time to get up to speed on how your air conditioner works so that you’ll be in the know when you take your next stroll in the park.
I’m going to give an intermediate explanation of the refrigeration cycle here, so if you’d like to take a step back and start with a more basic one, see this explanation of how an air conditioner works I wrote for lay people. (Another good article that covers basics of the refrigeration cycle as well as answers to some commonly asked questions is Martin Holladay’s Air Conditioner Basics.) Today we go a little deeper, though. I’ll name the parts of the refrigeration cycle and talk a bit more about the changes in the refrigerant as it goes through the cycle.
Still, there’s a lot I’m not going to cover in this article. I’m not going into the technical details of checking refrigerant levels, the properties of the different refrigerants used, how efficiency (SEER rating) is calculated, or any number of other important aspects of air conditioning systems.
The refrigeration cycle
The way your air conditioner pumps heat from inside to outside is through the refrigeration cycle, a thermodynamic cycle involving a special fluid — the refrigerant — that undergoes phase changes (between liquid and vapor), pressure changes, and temperature changes. The diagram below shows how the refrigerant flows through the air conditioning system and what’s happening along the way.
First, notice that the diagonal line shows which parts are inside the house and which parts are outside. If you have a split system, with the condensing unit sitting outside making noise and the air handler inside (which could mean in the crawl space or attic), the components are in different boxes. In a window AC or package unit, they’re all in the same box.
Now, let’s go through the four stages of the refrigeration cycle, one by one.
1. Evaporator coil
This is where the refrigerant picks up heat from inside the house. The evaporator coil is a copper tube, which carries the refrigerant, embedded in a framework of aluminum fins (photo below). Using this configuration, the refrigerant is connected to a lot of surface area that makes contact with the air blowing over it, which aids heat transfer from the air to the refrigerant. The most common geometry is the A-coil (below), but you also see flat coils and N-coils in some units.
The refrigerant comes into the evaporator coil as a liquid at a low temperature and low pressure. The air handler’s fan (a.k.a. the blower) blows air from the house across the coil. The evaporator coil is cold (about 40° F), and the air from the house is warm (about 75° F, depending on where you set your thermostat). Heat flows from warmer to cooler, so the air temperature drops, and the refrigerant picks up the heat lost by the air. This is the Second Law of Thermodynamics in action.
In addition to getting warmer, the refrigerant also changes phase here. It’s called the evaporator coil, after all, so the cold liquid refrigerant coming in evaporates and becomes a vapor. Phase changes are a great way to transfer heat because it takes a lot more heat to cause a phase change (especially between liquid an vapor) than it does to change the temperature of a material. Thus, when the refrigerant starts boiling, it really sucks up the BTUs (British Thermal Units).
One aspect of the flow may be confusing when you look at your air conditioner and try to figure out how the refrigerant flows from inside to outside. If you have a split system, the inside and outside pieces are connected by the refrigerant lines, often called simply the “line set.” These are two copper tubes, one larger and insulated tube (the suction line) running parallel to another smaller and uninsulated tube (the liquid line). When the vaporized refrigerant leaves the evaporator coil, it’s still fairly cold. Hence, the refrigerant going to the compressor outside is in the larger, insulated copper tube, not the smaller, warmer tube. As paradoxical as it seems, the colder tube is the one carrying the most heat. You can see that the suction line is the colder tube in the photo of the line set below because it even has frost on it, which is not normal and indicates a problem (e.g., incorrect amount of refrigerant or air flow over evaporator coil too low).
2. Compressor
When the refrigerant reaches the outdoor part of your air conditioner (photo at top), the compressor does exactly what its name suggests: it squishes the refrigerant down to a smaller volume, thus increasing the pressure and the temperature. Why? Because heat flows from warmer to cooler. You can’t get rid of heat from a cold refrigerant to 95° F air. The refrigerant has to be warmer than the outside air. That’s one reason why we need the compressor. The other is that the compressor is the pump that moves the refrigerant through the system.
3. Condenser coil
When the high pressure, high temperature, still-vaporized refrigerant leaves the compressor, it enters the condenser coil. As with the evaporator coil, it’s a copper tube embedded in aluminum fins that allows for efficient heat transfer. A fan inside the condensing unit pulls outdoor air through the sides of the coil and blows it out the top of the unit. Because of the work the compressor did, the refrigerant is hotter than the outdoor air. The Second Law of Thermodynamics kicks in here, and heat flows from the warmer refrigerant to the cooler outdoor air blowing over the condenser coil.
In the evaporator coil, refrigerant changes from liquid to vapor at a relatively low temperature. Now we’re dealing with higher temperatures, and the phase change reverses. If you’re confused by the phase change happening at different temperatures, think about what happens when you go to high altitudes. The air pressure is lower, and water boils at less than 212° F. Pressure changes affect the boiling/condensation point temperature, which is why boiling happens at a low temperature in the evaporator coil and condensation happens at a high temperature in the condenser coil.
After returning to the liquid state, the refrigerant travels through the liquid line (the hot, uninsulated copper tube) back to the indoor part of the air conditioner.
4. Expansion valve — where the magic happens
Once the refrigerant gets back to the indoor unit, it passes through a metering device, such as an expansion valve, and the magic of the refrigeration cycle happens here. The high pressure, relatively warm liquid runs into a constriction that doesn’t allow the refrigerant to pass through easily. As a result, when the liquid does get through to the other side, it finds itself in a much lower pressure. When the pressure drops like this, so does the temperature — a lot! This is what makes air conditioning possible. Without being able to get the refrigerant down to temperatures below the air in your home, an air conditioner wouldn’t be able to work. Why? Because heat flows from warmer to cooler, the old Second Law of Thermodynamics again.
After passing through the metering device, the refrigerant goes directly into the evaporator coil, and the cycle begins anew.
There you have it. If you followed what I wrote above, you’re ready to head out to the park benches.
*Well, OK, maybe I didn’t really overhear this conversation, but I swear I have been in parks and seen little old ladies talking on park benches.
REFRIGERANT TEMPERATURE
Allison - As you state above, "the refrigerant comes into the evaporator coil as a liquid at a low temperature and low pressure". Can a thermostat control the temperature of the refrigerant?
I certainly understand that a thermostat turns a unit on & off when the temperature in a room reaches the setting that the thermostat is set at.
But, could an end-user potentially control the temperature of the refrigerant?.........hence controlling the temperature of the air coming out of the supply ducts?
Thanks!
Response to Joseph Taormina
Most AC systems have only one mode of operation, and they're either on, operating at a given rate, or they're off. The thermostat in these systems tells them when to come on and go off. You have no control over temperature with them.
There are other systems, however, that have multi-stage or inverter-driven driven compressors that can modulate the flow of refrigerant. By changing the pressure in the system, which is what the compressor does, the temperatures at the different stages also change, but you wouldn't have direct control over this with your thermostat.
