Image Credit: Image #1: GBA
Image Credit: Image #1: GBA Base 65°F calculations are usually more accurate with 2x4 framed houses.
Image Credit: Images #2 and #3: Dana Dorsett Base 60°F calculations are usually more accurate with 2x6 framed houses.
Your old furnace or boiler is gasping its last breath and it’s time to pull the trigger on something newer, more reliable, and more efficient. How do you quickly size the new equipment?
If you leave the sizing calculations to HVAC contractors, most would replace the old furnace with equipment that has a comparable output rating. That would guarantee that you wouldn’t get cold, but at least 19 times out of 20, that would be a mistake.
Furnaces are routinely oversized
Most of the installed heating equipment in the U.S. is oversized. In fact, most equipment has a heat output that is between 2 and 4 times the heating load.
There are valid reasons to oversize the equipment a bit, but not by 2 to 4 times the load. Oversizing on that scale results in lower comfort and lower efficiency. Most people want enough capacity to cover somewhat colder temperatures “just in case” there is a cold snap or record low temperatures, or if they need to keep the house at 78°F for a frail elderly parent.
With the average installed equipment being 3 times oversized, that means you’re covered. But what are the consequences of this type of equipment oversizing?
What’s the 99% outdoor design temperature?
For a particular location, the “99% outdoor design temperature” is the temperature which is exceeded for 99% of the hours in an average year. In other words, only 1% of the hours in a year are colder than the 99% outdoor design temperature.
Heating appliances can be sized to meet a building’s heat load at the 99% outdoor design temperature or at the 99.6% outdoor design temperature. Building codes in the U.S. stipulate that every room be capable of being automatically heated to a minimum of 68°F at the 99% temperature bin for that location, making the 99% approach more relevant than the 99.6% approach. So it’s useful to know the “99% outdoor design temperature” for your location.
Three times larger than necessary? What does that mean?
A building’s heat load grows (approximately) linearly with the difference between indoor and outdoor temperatures (otherwise known as the delta-T). According to building code, a heating appliance is correctly sized when it is sufficient to cover the difference between 68°F and the outdoor design temperature.
For example, consider a house in Washington, D.C. (Climate Zone 4), where the outdoor design temperature is 20°F. If your furnace is oversized by a factor of 3, you could heat the house in a location with a delta-T that was three times larger than your actual delta-T of 48 F° — in other words, in a location with a delta-T of 144 F°. With that much capacity, the heating system won’t lose ground until the outside temperature drops below -76°F — an outdoor temperature not seen in Washington, D.C. since the last ice age!
That’s ridiculous, of course — but oversizing a furnace by a factor of 3 is the norm rather than the exception.
Oversizing a little is OK
The AFUE testing protocol (used to determine furnace efficiency) presumes an oversizing factor of 1.7 times, which still gives a large margin for colder weather — more than covering the absolute record low temperatures in most locations. When a furnace is oversized by a factor of 1.7, it isn’t so oversized that it impacts efficiency, but that much oversizing is really too much for multi-stage furnaces. A typical two-stage condensing gas furnace has a turn-down ratio of less than 2:1. With most of these furnaces, the low-fire output is still 60% or more of the high-fire output.
When a furnace with a low-fire rating of 60% is oversized by a factor of 1.7, you could cover 99% of the building’s heating needs at low fire. You might as well hard-wire the furnace so that it never steps up to high-fire mode.
For comfort and efficiency, ASHRAE recommends that heating equipment be sized at 1.4 times the design heat load.
At 1.4 times oversizing, the house in the example above would have its heating load fully covered at a temperature difference of (1.4 x 48 F°) = 67 F°. With a delta-T of 67 F°, the heating system is adequate when the outdoor temperature drops to (68°F – 67 F°) = 1°F, which is 19 F° colder than the 99% outside design temperature. But that’s an outdoor temperature that may actually occur a few times over the 15-to-25 year lifecycle of the heating equipment (but not every year). When that happens it’s only for brief periods of time — short enough that the thermal mass of the house keeps it from losing much ground. So there is usually no comfort problem.
Methods for calculating a building’s heat load
That’s the target for sizing equipment. But to get to this target, it’s important to come up with a reasonably accurate design heat load number.
You could measure up the windows and walls, estimate the U-factors of different building assemblies, and run an I=B=R load calculation on the whole house, or you could even run a Manual J calculation. But those methods take time, and it’s easy to make errors when estimating the U-factors of components of an older house. It’s human nature to err to the high side when in doubt, which is also a mistake.
Fortunately, if you have access to historical fuel purchase history, you don’t have to guess.
You can calculate a building’s heat load in 15 minutes
You have instrumentation already in the house that is measuring the heat load: namely, the existing heating equipment. The way to use it for measurement purposes is:
- Take a mid- to late-winter fuel bill, and note the exact dates covered by the bill — the fill-up dates or the meter-reading dates.
- Look for a specification label on your furnace or boiler that includes the input BTU/h rating and the output BTU/h rating for your equipment.
- Download base 65°F or base 60°F heating degree-day spreadsheets covering those dates for a nearby weather station from a website called DegreeDays.net.
- Look up the 99% outside design temperature (sometimes called the “heating 99% dry bulb temperature”) for your location from a website — for example, from an online document called Manual J Outdoor Design Conditions for Residential Load Calculation.
Now you have enough information to estimate your building’s heat load with reasonable accuracy, independent of the house construction details.
For example, assume that a house in Washington, D.C. (where the outdoor design temperature is 20°F) used 182 therms of natural gas between January 6 and February 8.
If the gas furnace nameplate shows an input rating of 110,000 BTU/h and an output rating of 88,000 BTU/h, you can use those numbers to determine the furnace’s thermal efficiency — in this case, 80%.
Multiply the input fuel amount by the efficiency of the equipment to determine how much heat was delivered to the building.
ENERGY CONTENT OF FUELS
Natural gas: 1,000 BTU/cu. ft.Propane: 91,333 to 93,000 BTU/gallonFuel oil: 138,700 to 140,000 BTU/gallonKerosene: 120,000 to 135,000 BTU/gallon
To calculate the net amount of heat that was delivered into the ducts (or into the heating pipes if we are talking about a boiler), take the number of therms indicated on your fuel bill and multiply it by the equipment efficiency:
182 therms x (88,000/111,000) = 145.6 therms
Then multiply therms by 100,000 (the number of BTU per therm) to convert therms to BTU:
145.6 therms (x 100,000 BTU/therm) = 14.56 million BTU (MMBTU).
Next, download and sum up the daily base 65°F heating degree days (HDD) for the nearest weather station — in this case, from station KDCA: Washington National Airport, Virginia — from the DegreeDays.net web site for the period of January 6 through February 7. (Include only one of the meter-reading dates, not both.) In this example, the sum comes to 937.7 HDD-65°F. (See Image #2, below.)
Next, download and sum the date for base 60°F. The result is 772.9 HDD-60°F. (See Image #3, below.)
14.56 MMBTU / 937.7 HDD is 15,527 BTU per degree-day. With 24 hours in a day, that’s an average of 647 BTU per degree-hour at a balance point of 65°F.
14.56 MMBTU / 772.9 HDD is 18,838 BTU per degree-day, and with 24 hours in a day that’s an average of 785 BTU per degree-hour at a balance point of 60°F.
A balance point of 65°F with design temp of 20°F is a difference of 45 F° degrees, and the implied heat load is then 45 F° x 647 BTU/F-hr = ~29,115 BTU/hr.
At a balance point of 60°F there are only 40 F° heating degrees, and the implied load is 45 F° x 785 BTU/F-hr = ~31,400 BTU/hr.
That’s a range of about 8% between the calculation based on 65°F heating degree days and the calculation based on 60°F heating degree days. Which is closest to reality?
It depends. Most 2×4 framed houses will have a balance point close to 65°F, most 2×6 framed houses will balance closer to 60°F. But unless it’s a superinsulated house, it’s likely balance point is somewhere in that range.
Comparing 65°F HDD calculations with 60°F HDD calculations
At this point, you may be thinking, “Why would the calculated heating load for a house with 2×4 walls (29,155 BTU/h) be lower than the calculated heating load for a house with 2×6 walls (31,400 BTU/h)?”
The short answer is, “Both calculations assume that you’ve used the same amount of fuel over the average outdoor temperatures during the period in question, which yields a higher BTU per degree-hour constant for the house with 2×6 walls.”
Put another way, if the better-insulated house used the same amount of fuel during the same weather conditions, its load is going to be higher when it’s really cold out. If two identical houses were built, one with 2×4 walls and the other with 2×6 walls, the 2×6 house should have used less fuel at the average outdoor temperature over the period, not the same amount of fuel. But if different 2×4 and 2×6 houses use the same amount of fuel, the incremental heat requirement of the 2×6 house per degree will be bigger. When you then use that bigger load per-degree constant to predict the load at the outside design temperature, the calculation results in a bigger number.
What about thermostat settings?
If the average indoor temperature was kept substantially below 68°F, you can account for that fact by dropping the degree-day base.
For example, if you normally keep the thermostat at 62°F rather than 68°F, subtract 6 F° from the temperature bases to get the BTU/degree-hour constant, but add 6 F° to the total heating degrees when you run the final number to be sure it meets code when sizing the equipment.
Error factors
The heat load calculated from the difference in temperature from the balance point isn’t a perfectly linear BTU/degree-hour constant as implied by this calculation method. There is an offset related to the internal heat sources like electrical plug loads and warm bodies. But the error from the difference in slope between the linear approximation from a presumptive balance point method shown here and other methods — for example, an I=B=R linear model (based on the indoor temperature) or a more nuanced Manual-J calculation — doesn’t induce a large error when wintertime data are used.
If the same heating fuel is also used for domestic hot water, this calculation method exaggerates the implied load numbers, since some of that fuel was used by the water heater and sent down the drain. But some of the space heating came via solar gains that would reduce the implied load numbers. These errors tend to balance each other out to a greater or lesser degree.
If you spent 10 days on the beach in Belize during that period, with your home thermostat set to 50°F, use a different billing period.
If an auxiliary heating appliance was being used on a regular basis (say, a wood stove or a ductless minisplit), this calculation method will be too far from reality to be useful. If that’s the case, go back to I=B=R or Manual-J.
In some cases, your heating equipment may be old, decrepit, and not performing very near its original name plate efficiency. That would skew the calculated number to something higher than reality, but it would have to be pretty far off to make a meaningful difference. If that’s the case, calculate it using some lower efficiency. Even a 100-year-old steam boiler is usually still delivering at least 55% efficiency, and often 65-70%.
Equipment sizing
Unless there is an obvious large error factor that skews the result badly, move on:
For sizing the equipment, use the ASHRAE 1.4x sizing factor:
1.4 x 29,115 BTU/hr = 40,761 BTU/hr (with a 65°F balance point assumption)
1.4 x 31,400 BTU/hr = 43,960 BTU/hr (with a 60°F balance point assumption)
If reality happens to be the 60°F balance point — the 31,400 BTU/h implied load number — then using the 1.4x multiplier on the lower 65°F implied load of 29,115 BTU/h yields about 40,761 BTU/h, in which case you’re even covered for the higher implied load with ample margin. Since older equipment probably isn’t fully as efficient as it was when it was new, equipment rated at 40,000 BTU/h should be good enough.
But if you got nervous and sized it at 50,000 BTU/h of output, it would still be only ~1.7x oversized for the lower 29,115 BTU/h estimate, which means it would hit its AFUE efficiency number (even though it would be bigger than ideal). From a practical point of view, any heating appliance with an output between 40,000-50,000 BTU/h will be fine.
The highest comfort occurs when it’s cold out, when the equipment is actually running and delivering steady heat — rather than running for a while and overshooting the thermostat, with a long cooling off period between cycles. If the new equipment is multi-stage or modulating, it’s best if the lowest stage output is well under the 29,000 BTU/h load, so that the firing range is meaningful.
With boilers, use only the DOE output rating for the equipment; ignore the net I=B=R numbers. The fuel use calculation has the distribution and idling losses included — they can’t be separated out. (There are other factors that come into play when dealing with modulating condensing boilers, but that’s a topic for another day.) If the replacement equipment will be a heat pump, consult the extended temperature range tables for its output at the 99% design temperature.
Whatever the equipment type, have the load numbers and minimum / maximum output numbers in hand before talking to an HVAC contractor.
Expect pushback from contractors
HVAC contractors have become accustomed to installing oversized equipment, and may even think that equipment really needs to be that big. But you don’t have to follow them down the rabbit hole.
Have confidence in your fuel use numbers. This calculation method is better than an estimate; it’s a measurement.
If you push back, some contractors will balk or refuse to bid equipment that small. (Good riddance!) Others will want you to sign a waiver. (OK — but really?!)
Still others will understand that a lipstick-on-mirror fuel-use calculation is sufficiently close to reality that they’ll just go with it if you direct them to.
Typical arguments heard from contractors are rules of thumb such as: “It needs to be at least 25 BTU/h per square foot of living space. Your house is 2,400 square feet, so that’s 60,000. Let’s bump it to 75,000 just in case it gets cold out.”
Which reliably oversized most houses by at least 2x. Or: “It needs to be at least 90,000 BTU/h or it’ll take forever to return from overnight setback.”
Which is almost never true.
Recent feedback from a contractor insisting on a 100,000 BTU/h condensing boiler for a house with a design heat load under 30,000 BTU/h (based on fuel use calculations and later verified by Manual-J) went, “It needs to be at least 100,000 BTU/h or it’ll take forever to bring the house up to temperature after you’ve been out of power for a few days.”
Out of power for days? How often does that happen each winter (or decade)?
Every day, contractors come up with new creative reasons for oversizing. But with the load calculation in your back pocket, you don’t have to accept these arguments.
_________________________________________________________________________
Dana Dorsett has lifelong interests in energy policy, building science, and home efficiency. He is currently an electrical engineer in Massachusetts.
62 Comments
Keep it simple
If you have a furnace of known efficiency you can also do this. On a still and cloudy day you can time the hourly furnace run times, take this fraction times the furnace output for an hourly Btu usage. Divide this by the Delta T for the hourly Btu heat loss per degree F. Now with this information you find the design temperature heat loss. If you do a deep nightly temperature setback you will find a furnace oversizing by a factor of 2 is just about right.
Hi @user-723121,
This seems like a better method than fuel use, since it measures the furnace operation only and doesn't get distorted by fuel use of other gas appliances in the house (water heater, bbq in my case).
I want to make sure I'm understanding the calculation as I'm just a homeowner not an hvac engineer...
Example:
December 4 had a mean outdoor temperature of 29.8F.
Furnace ran 6 hrs
6 / 24 hr * 45,000 BTU/h = 11,259 BTU/h for December 4.
I did the same calculation for 3 other days with different runtimes / outdoor temperatures and plotted them. I then got an "actual" heat loss: https://s3.amazonaws.com/greenbuildingadvisor.s3.tauntoncloud.com/app/uploads/2022/12/20113738/48563_1671554258_energy-chart.png
Is this the right way?
It's nearly the exact same method - usually the ancillary gas usage is small enough to be irrelevant since the delta between furnace sizes is large.
Thanks Paul. In that case, the thermostat runtime method is just easier for me to understand... Assuming I did it correctly!
Thermostat run times are only useful when using fixed-output boilers/furnaces. With 1 & 2 stage or modulating equipment there is a significant difference between the maximum modulated BTU/hr rate and the minimum or average rate.
It gets even more complicated with multi-stage or modulating condensing equipment, since the efficiency is not the same across output temperature.
When all else fails, if you can run a tape measure it's not hard to use the stripped-down Manual-J load calculation tool from BetterBuiltNW:
https://betterbuiltnw.com/hvac-sizing-tool
It's so easy to use that even HVAC contractors can use it without screwing it up too badly. (But the more idiot proof you make something the more creative the idiots become. Don't be an idiot screwing with the number for the "just in case it's actually worse than that" on the input parameters.)
The tool is free, but you do need to give up an email to them (which they do NOT resell).
That tool was designed by a consortium of utility companies in the Pacific Northwest specifically for ease of use for sizing heat pumps, after suffering through years of comfort & efficiency complaints from ratepayers who had participated in their heat pump programs. The majority of those problems stemmed from oversized equipment installed by HVAC contractors who had NOT run proper load calculations (which is, alas, the major fraction of HVAC contractors.)
I'm currently in the process of getting proposals for swapping out my own gas-burning hydronic heating system for heat pump solutions, and there is no way I'd let the contractors run their own numbers. Even before a site visit I email them a room by room IBR load calculation, along with the radiation list, and some radiation upgrades list to ensure that it will still work at design temp at an average water temp of 110F (currently running ~125F). The best (if quite pricey) proposal so far is for the SpacePak Solstice cold climate hydronic heat pump, which is made in Westfield, Massachusetts with mostly US components (most critical parts are stocked at local heating & plumbing supply houses, not Singapore or Seoul), and doesn't have the supply chain and availability & support issues of the Asian competition (LG has a great full VRF system, but support is thin. Samsung has a similar VRF system, but doesn't ship the hydronic output part to the US yet. ) It uses a cold climate type vapor injection compressor, and has a rated output all the way down to -22F/-30C.
I'm still waiting on proposals for LG Multi-Vs solutions. I only wish Daikin & Mitsubishi et al had a US presence for some of the better monobloc hydronic heat pumps they are marketing in Europe, but even so the SpacePak Solstice beats them on raw efficiency & capacity when outdoor temps are in the single digits (or below 0F.)
If you've bothered read this far I'll go ahead and share more about the SpacePak solution. I'm targeting an average water temp of 110F on the radiation, a temp at which the Solstice delivers a raw COP of about 3 at my design temp of +5F, with about 15% of capacity margin for my home's heat load:
https://www.spacepak.com/Themes/SpacePakTheme/images/gallery/ILAHP%20113%20leaving%20water.svg
At other temps the capacity & efficiency does vary:
https://www.spacepak.com/solstice-inverter-extreme#documents
With a pumping power adder the system COP will probably be just shy of 3 @ +5F, but the seasonal efficiency will likely beat the average ground source heat pump solution from a decade ago (but probably not beat a well designed WaterFurnace 7 modulating GSHP.) I would expect the average seasonal efficiency to be comparable to the best-in-class ductless mini-split solutions. But with heat pump + buffer tank + high-velocity cooling air handlers it's quite a bit more expensive than a mini-split/multi-split solution (that wouldn't fit well in my house anyway.)
You can also look at your monthly gas usage and determine what is being used monthly in the non heating season (summer months). Subtract this average from your winter monthly usage for quite an accurate heating use only figure. Quite easy to do monthly gas meter readings coupled with Heating Degree Days for the period to get the heat loss for your house in Btu's per degree F. This number can then aid in sizing HVAC equipment using the Design Temperature for your location. Equipment efficiency must be factored in the calculation. You will find you are using less gas on a HDD basis as the daylength increases, yes the sun does make a difference.
Doug
Thank you Dana, I enjoyed reading your reply! Good luck with your heat pump conversion. The equipment you found with a COP of 3 at 5F is awesome. The systems I have been looking at for my forced air system only manage a COP of around 2 at that temperature.
Indeed I do have a single stage, single speed furnace (1994 Lennox G26), which is why I believe the thermostat runtime report is the quickest and most accurate method for me to create a load chart. I did also use the better built tool (this shows up as the 'modelled' load line on the chart I attached above). The results from that tool lined up quite well with the load calc that was provided in my energy audit. The tool is indeed excellently made (I design web applications for a living). I also used a 3rd tool that is free from the government of Canada called HOT2000 (lol) and had an energy audit done.
At my location's winter design temp (1F), the software models and the energy audit say that my heating load is between 32,500 and 37,500 BTU/h. My thermostat runtime calculation tells me that it is 25,000 BTU/h. I am thinking of getting a 24,000 BTU/h heat pump plus a 96% efficient 2-stage backup gas furnace of 40,000 BTU/h. What do you think? I have a forced air system (I would love hydronic in floor heat - maybe in a future house!)
Yeah it's usually easier to use the meter, but now that some furnaces easily display the runtimes, they can be used.
I personally would never advise going with a dual-fuel system, since they're something of a kludge, adding complexity without much real benefit. Either the fossil-burner is heating or the heat pump is heating- they can't work together as a team simultaneously. With most ducted heat pumps most of the heat will be coming from the heat pump even while the resistive heat strips are engaged. With an average COP >1 it's still more efficient than heat-strip alone.
Most heat pumps are sized by their nominal AHRI cooling capacity. Their heating capacity varies (a LOT) relative to their rated cooling power, especially heat pumps with modulating vap0r-injection compressors, with extends both capacity & efficiency at lower temps. Most "cold climate" heat pumps based on that technology would have 20-25% more heating capacity at +5F than their AHRI cooling capacity, ductless usually more than ducted. A ductless 24,000 BTU/hr cold climate heat pump would deliver on the order of 30,000 BTU/hr @ +1F outside. But it varies all over the place by vendor & model.
A good place to search for potential cold climate heat pump solutions is NEEP's heat pump database, which is searchable by type. See:
https://ashp.neep.org/#!/product_list/
If you select "Single Zone Ducted, Centrally Ducted" from the pull down menu in the middle, and set the "Heating Capacity 5℉ " slider on the upper right from 80,000 BTU/hr down to 40,ooo BTU/hr, and the "Heating Capacity 47℉" slider from 0F up to 35,000 BTU/hr, there are many potential solutions, which can be narrowed further by vendor name. Something like Samsung's nominal 30 ton (cooling) AC036BXSCCH/AC036BNZDCH combination is probably a good fit, and would need NO gas fired backup (though you might want some resistance strip heat for when it's in negative double digits.)
https://ashp.neep.org/#!/product/65659/7/25000///0
That unit has about a 4:1 turn-down ratio @47F, which means it would modulate most of the season even if your real 99% heat load is closer to the 25,000 BTU/hr number.
There are others- go exploring!
In my area there have been supply chain issues getting the full range of Mitsubishi models, even though their northeastern regional design center is less than a 30 minute drive from my house. Clearly YMMV
Scuttlebutt passed on by one of the contractors I've been talking with indicates that it's much easier to get Samsung product than LG/Fujitsu/Mitsubishi, and that the quality & depth of their lineup has improved considerably in recent years, and many contractors who used to install a lot of Mitsubishi equipment are now looking to Samsung as their go-to product lines, since they can actually get them. Other sources (unverified) have indicated that many or most Samsung units are now designed and built by the huge Chinese company Midea, now the world's largest air conditioning equipment vendor. Midea makes most of Carrier's modulating heat pumps and ductless equipment too, or the innards thereof (verified), having been in bed together for something like a decade now.
Thanks again Dana... I have spent too many hours on the neep site :) I have definitely noticed what you said about heating capacity being quite different than cooling. Some units which I really liked, such as the Trane XV19, have very poor heat capacity at lower temperatures.
I am somewhat limited here too, by what my local hvac companies carry and install. I'm also limited by the systems that qualify for a rebate under our Canadian "greener homes" program. But I am not done with my research yet and new systems are added to the rebate program every quarter!
I will have to look into the Samsung models you mention as I haven't come across it yet. I generally try to avoid Samsung as I've read some terrible stories about their appliances and have had personal bad experience with their computer monitors/TVs.
Carrier systems are very common around here. I had at least 4 quotes for the same Carrier hybrid system which includes a 38MARBQ heat pump (Midea with Carrier name on it). This heat pump has good output at low temperatures. However I am not thrilled about the fact that Carrier has handicapped this system to run at a fixed fan speed despite the heat pump being variable. So my research continues...
I met a new hvac contractor recently who deals with mitsubishi so I am looking forward to seeing proposals from him.
I am surprised to have learned that a hybrid system is cheaper than all-electric by a few thousand and I do like the 'hot heat' given off by a gas furnace during the dead of winter. However I also like the fact that a heat pump will handle most of the heating and reduce my gas use by a huge amount, so hybrid is actually appealing to me. A furnace + heat pump is also not really that different in complexity than my current furnace + A/C unit. But I do agree that a heat pump + air handler is a bit more elegant, and I may still go that route if the pricing makes sense.
I created a comparison chart (https://s3.amazonaws.com/greenbuildingadvisor.s3.tauntoncloud.com/app/uploads/2022/12/22095837/48563_1671721116_heat-pump-comparison.png) of heat pumps using their max heat capacity and energy consumption at 17F. Each bubble's size represents that unit's COP. I'll have to throw in the Samsung and see how it compares :) But it seems that there is a general trade-off between COP and heating capacity. Perhaps this will change over time as technology improves.
Following up as we've been through the worst of winter with my old furnace :)
I ran the fuel use calculations and came to 27,997 BTU/h. This is a bit more than the 24,500 BTU/h estimate from furnace runtime but makes sense since I also have a gas water heater.
Based on this I am very confident to tell my hvac contractor what size equipment I need.
Thank you again for a great article.
Hi Tkzz, as an REA in Ontario I'm very interested by your efforts to calculate your home's heating and cooling loads. I've recently gone down the rabbit hole looking to understand how to best advise homeowners. Your experience with the various methods to calculate heating/cooling loads would be invaluable. Would you be willing to connect with me for a chat?
Efficiency loss
What is a typical efficiency loss for an over-sized system? and how does that loss relate to how badly the system is over-sized?
Response to Daniel Beideck
Daniel,
For the most part, the idea that oversized equipment results in a big efficiency hit is a myth.
I addressed the issue in one of my articles, Saving Energy With Manual J and Manual D. In that article, I wrote:
"There are strong arguments against routine oversizing of HVAC equipment. The best argument is simple: oversized equipment usually costs more than right-sized equipment.
"Oversized equipment suffers from short cycling. For example, an oversized furnace brings a home up to temperature quickly, and then shuts off. A few minutes later, it comes on again, only to shut off quickly. Many homeowners find the see-saw sound of a short-cycling furnace to be annoying. ...
"Increasing evidence shows that energy experts have exaggerated the negative effects of equipment oversizing, however. Studies have confirmed that oversized furnaces don't use any more energy than right-sized furnaces. Moreover, newer modulating or two-speed furnaces operate efficiently under part-load conditions, solving any possible problems from furnace oversizing.
"Although there are ample reasons to believe that oversized air conditioners are less effective than right-sized equipment at dehumidification, at least one field study was unable to measure any performance improvements or energy savings after replacing an existing oversized air conditioner with a new right-sized unit."
For more discussion of these issues, see the comments section below that article.
@ Daniel
One thing oversizing does is cause rapid cycling as Martin stated, which leads to faster component wear, igniters, motors, sensors last longer when they are run for longer periods and shut down/restarted less frequently.
Summary
I am attempting to digest this article and several others, such as the one Martin references in #3 and some posts on Allison Bailes blog, to determine which facts there is broad agreement on and which facts are disputed. Would others agree with the following summary:
For gas furnaces, unlike air conditioners and heat pumps, efficiency does not vary by much when the equipment operates at partial capacity. It appears that there is broad agreement that oversizing up to about 1.5 is good and that oversizing by more than about 2.0 is bad. (Those values would shift higher for equipment with wide modulation ranges.) The disagreement seems to be over how bad it is. Some seem to feel that there is an oversizing epidemic that we need to combat. Others seem to feel that this is pretty far down the list of priorities.
The advantages of oversizing, which are fully obtained with only modest oversizing, are:
i) handling especially severe weather
ii) faster recovery from a thermostat setback
iii) for two-stage or modulating heat pumps and air conditioners, improved efficiency due to more frequent operation at partial capacity
The disadvantages of oversizing are:
i) equipment costs
ii) requires either larger ducting or operation at higher static pressures
iii) larger temperature swings due to short bursts of hot or cool air or due to minimum run times
iv) for air conditioners, reduced ability to remove humidity
v) reduced equipment life due to frequent cycling
The disagreements seem to be over the magnitude of these problems. All seem to agree that two-stage or modulating equipment mitigates these problems (except cost), although many would argue that they don't solve these problems.
Thermostat settings
One way to prevent short cycling of heating equipment is to lower the thermostat cycles per hour. For our 2 stage, 95% furnace I like 3 cycles per hour. Once the house is up to temperature in the morning the furnace will just run on low fire and the DC fan motor on low speed, very quiet.
An analogous method for estimating cooling load?
Dana,
Very nice article. I just used this method to confirm that the method my supply house recommended 12 years ago did indeed result in a 2.5x oversized boiler. I'm trying to size some mini-splits for this house now, primarily for cooling, but also for backup heat in the event of a boiler failure, and I'm wondering if you have a similar method for that? We cool now using window units, which are relatively new and have an eer of 10-11.
@ Reid
What i don't like about two stage is the dumb logic, my furnace decides on its own when to go into high fire, and somehow it always decides to go to second stage then the thermostat shuts it down less then 30 secs later (sometimes less then 5 secs later). I assume this is causing faster component wear. I can't make any adjustments to this, thermostat does not have a fire set number of times an hour option, the furnace has no high fire adjustments except on or off (i can disable the high fire completely). My house load is calculated as 45k, the furnace is 40k (i did undersize it but am planning on further insulation/air sealing to bring load to 30k in the future) and the stages are 25/39k out.
It is a new thermostat with the furnace, programmable (which was more trouble then it was worth since i am on varying schedules) but does not have the option to select low/high fire. Perhaps there are replacement thermostats with more features when i can afford to replace it.
@ Alan B
There are others on this forum that know way more about HVAC equipment than I do. My knowledge is based on what I have read here and looking through the manuals for equipment I am considering for my house.
There are single stage thermostats and two stage thermostats. When you use a two stage furnace with a single stage thermostat, the only information that the furnace has is whether or not the thermostat is calling for heat. It assumes that it needs to go to high heat if the current heat call has continued for more than a threshold time. That threshold might be adjustable - your manual would say. The furnace has no idea how much longer the heat call will likely continue. A two stage thermostat has more information available - the current measured temperature. Therefore, it would at least be feasible for it to use more intelligent logic. You can read the manuals for many thermostats online to find out what logic they use.
We are going to use a zoning system that has logic to intervene between the several thermostats and the furnace. Various algorithms are possible there. The one I expect we will use changes to second stage based on the number of zones that are calling for heat. For each alternative algorithm, there is some scenario in which it does something suboptimal.
Link to Allison Bailes's article
Here is a link to the article by Allison Bailes that Dana mentioned -- the one where Allison explains how to time the cycles of your air conditioner on a hot day to see if your air conditioner is correctly sized: How to Tell If Your Air Conditioner Is Oversized.
Oversizing costs
The efficiency hit varies with equipment type, but is much more pronounces with zoned systems than single zone systems. Hot air furnaces suffer very little efficiency loss even at 5x oversizing, but there's a very real comfort disadvantage to that. The fairly flat efficiency response is partly due to the very low thermal mass of hot air systems, but there is still higher distribution losses due to larger duct surface area, and slightly more power use (that doesn't show up an a fuel use analysis) due to the higher air handler power required.
Most 2-stage hot air systems use a dumb timer to decide when to step up to the second stage. One of the people in my office lives in a town house development with identical 2- stage ~80,000 BTU/hr gas hot air furnaces, yet the design temp heat load of even the largest units is under 40,000 BTU/hr. With retrofit air sealing and new window his is now about 15,000 BTU/hr. Those furnaces always step up to high-fire whenever the call for heat has been longer than ~10 minutes, so when using deep overnight setbacks they always finish at high fire. Annoyed with the hot-blast and lower efficiency he dug into the service operation and like Reid figured out how to hard-wire the controls to never step up to high fire, but it was not a vendor approved hack, and thus voids the equipment warranty.
Hydronic systems with mid to high-mass boilers experience very dramatic efficiency losses with oversizing due to standby losses from both the boiler jacket and distribution system. If multi-zoned these losses are magnified, since the boiler losses are the same whether serving one small zone or the whole house. Take a look a the regression curves for the different boiler system types in this bit of boiler testing done at Brookhaven National Labs about a decade back:
https://www.bnl.gov/isd/documents/41399.pdf
If the boiler is 3x oversized, even at the 99% design condition the efficiency will be at the 33% mark on the curve, and the average seasonal load will be below the 15% tick. With heat purging controls the shoulder of the curve moves to the left, which helps (a lot, of only 3x oversized). Some mid-mass boilers have smarter heat purging controls, most don't. If 1.4x oversized per ASHRAE it's running at about the 70% of max output level at the 99% outside design temp, and the average load is around the 33% mark, which isn't terrible, and not over the efficiency cliff. The tabulated results at 3x & 2x oversizing are found in Table 3, p.9.
It's easy to naively think that modulating condensing boiler will solve this problem, but oversizing modulating boilers present a more complex set of problems that I intend to follow up with in a separate blog article. There are many modulating condensing boilers installed that neither modulate nor condense due to their oversizing factors, and surprisingly few optimally sized for the loads, particularly on multi-zoned systems.
There isn't a similarly simple way to calculate air conditioner oversizing, but if you're home during peak cooling hours you can time the duty cycling to come up with reasonable estimates. Unlike peak heating loads, the the peak cooling hours aren't well correlated with peak outdoor temperature, and far more correlated with peak solar gain. Houses with a lot of west facing windows will usually see peak cooling loads hours after the peak outdoor temperature. I believe Allison Bailes III had a blog piece that detailed how he measured the duty cycle on the AC to come up with the oversizing factor a year or two ago.
Reid's Summary
I want to add to Reid's summary an additional disadvantage:
*Noisier operation, and more noticeable noise because of the cycling.
If we are keeping track Dana also added two items:
*Higher duct heat losses due to larger duct surface area
*Issues are a little different and penalties higher for hydronic.
Dana, thanks for writing this. It's good to have it written up where people can refer to it.
Alan B
Alan,
Some 2 stage furnaces have a switch on them as to when the furnace goes from low fire to high fire. Our Lennox furnace came from the factory set at 10 minutes, I changed it to the 15 minute setting. It was a small yellow dip switch called (2nd stage delay) on the main circuit board. There are thermostats with adjustable temperature differential settings allowing the furnace to run longer less often, even the most basic Honeywell digital thermostats have a (cycles per hour setting).
Sizing Replacement HVAC
Though this article deals exclusively with replacement heating equipment, it would be worth a mention that replacing combined heating and cooling equipment requires a different approach.
Measure that reduce comfort need not apply.
Heating systems are most comfortable when they're actively running. Limiting cycles per hour or expanding the differential temperature swings may improve as-used efficiency, but degrades comfort. At the end of the day the measures that increase the temperature swings are the opposite of what you're seeking with heating system. When you right-size the system the duty cycles are longer the colder it gets, and you can keep the differential temperature band reasonably narrow, which increases.
If a furnace is less then 1.4x oversized for the 99% outside design temp the run times would always be reasonably long, and you wouldn't need to limit the cycles per hour or mess around with second-stage delays or otherwise open up the temperature differential. Having more flexibility on programming for 2 stage equipment would be useful though.
The method only defines the heating load, true (@ Leon Meyers )
But knowing the heating load is at least a start, and would be an important piece to know when looking at combined solutions.
Heat pump solutions aren't always in a reasonable range for both heating and cooling, often oversized for one or the other (and all too often, oversized for both) nor are many pre-packaged gas + cooling coil solutions.
Excellent Article
I wish I had read your article five years ago before having new heating and A/C installed. I contacted about five contractors and none of them would do Manual J, or anything else. I tried to do a sort of Manual J using an on-line program. I would have felt a lot more confident when talking to contractors if I had used your calculations to see how well they agreed with my manual J calculations.
Others sources of degree-day data?
Dana, Do you know of any no-cost databases for accessing degree-day data (or, I suppose, hourly historical temperature data from which degree-days could be computed)? I was thinking of writing an app that would do the calculation that you describe. The degree-days web interface is free of course, but their API access requires a substantial subscription fee.
Sorry, don't know of any freebies.
I'm not sure if there is NWS weather station data or other that would be any cheaper than the degreedays.net / wunderground.com , or that would have the same very-local coverage.
I haven't tried out degreedays.net's linear regression tool (currently in beta testing) for determining the degree base with the best fit, but if you were going to write an app that would be a useful for getting higher precision on the load estimates than simply bracketing it between presumptive 60F & 65F base temperatures. (Not that higher precision is actually needed in most cases.)
http://www.degreedays.net/regression-analysis
Simple
Finally had time to read this in full. What a simple and elegant method. Another good blog Dana.
Useful analysis
I tried Dana’s heating system sizing method on an oil furnace (used for both hot water and space heating) at my girlfriend’s 1,400 SQFT circa 1979 ranch. I used the six oil deliveries (since she’s owned the place) to calculate five analyses of oil usage.
• I looked up BTU’s per gallon of #2 heating oil (138,000), since Dana’s calculations used gas (100,000 BTUs/therm).
• The heating (and hot water heating) boiler on my girlfriend’s home is oversized by about 3.6 times, the range Dana notes is typical oversizing.
• Four of five results were based on the home with about R-20 ceiling insulation, 2x4 walls, R-11 batts under the floor, and single-pane windows with storm windows. The fifth analysis was after ceiling insulation was increased to about R-50, plus ceiling and door air-sealing. The energy-saving improvements cut space heating costs by about 30%. That’s more than I expected.
• One analysis covers the Fall/Summer/Spring seasons, and could be used to estimate hot water heating. It appears that hot water accounts for about one fifth of the oil usage, seems reasonable.
• The BTUs per Heating Degree Day for the three other winter periods were within a plus or minus 12% range, without taking into account the hot water heating and solar gain variables.
Now we can do some homework in advance to be prepared when the old dinosaur boiler does suddenly fail. Rather than duplicate the 110,000 BTU/hr output, we could substitute a 30,000 BTU/hr boiler. I’d prefer to keep the hot water heating system separate for a number of reasons.
Thanks Dana for this useful article!
I'm glad it worked for you!
The energy content of alternate fuels is in the side-bar mid-way through the article, if you didn't catch it.
The hard part is finding a 30,000 BTU/hr output oil boiler. The smallest jets on oil-burners in the US are typically 0.5gph (about 68-70,000 BTU/hr in), and those often gum up & clog on the fuels available in the US. That would still be ~2x oversized for you space heating load. To use a boiler at that ovesizing factor efficiently requires using heat-purging controls. Sometimes it works more efficiently if rather than running the hot water separately, an indirect hot water heater is used to take advantage of it's thermal mass. Boilers such as the System 2000 EK1 Frontier can be jetted as low as 0.68 gph, and the contrlos use an indirect hot water heater as the heat dump for purging heat from the boiler at the end of a burn, which turns out to be quite effective:
http://energykinetics.com/wp-content/uploads/2015/10/specification-EK1-EK2-OilHeat.pdf
The smallest Burnham MPO-IQ 84 also has smart heat purging controls, and can be jetted at 0.60 gph. It also has internal self-protection from low return water temperatures I(down to 110F, IIRC) which can be an issue when down-sizing oil boilers.
https://file.ac/RPLC0KQp6es/MPO-IQ%20Product%20Data%20Sheet.pdf
Measuring up the radiation to estimate the return water temperature is important when down sizing an oil boiler. At entering water temps temps (EWT) below 140F many oil boilers will be destroyed by acidic exhaust condensation on the heat exchangers, and even at 140F EWT there can be substantial flue condensation to manage, much more so than with older-80-83% efficiency oil boilers.
If the existing boiler has a lot of life left to it, at 3x oversizing a heat purging retrofit economizer such as the Intellicon 3250/HW+ can make a measurable difference in fuel use: http://www.intellidynellc.com/index.php/products/heating/hw
Of course, knowing the heat load also allows you to figure out right-sized alternatives, such as high-efficiency heat pumps. A ~30K heat load is within the output range of 2-2.5 tons of cold climate mini-split/multi-split in most US locations. Whether or not that's currently a higher or lower carbon solution than another oil boiler depends quite bit on your local grid's carbon foot print, and how you expect it to evolve over the next 15-25 years.
https://www.greenbuildingadvisor.com/blogs/dept/guest-blogs/carbon-footprint-minisplits
wind
Note that the fuel use method assumes average wind - high winds occur and can add considerable load. Hopefully this is covered by the 40% margin.
While cycles cause wear on equipment, so does the number of operating hours - which is lower with larger equipment.
My somewhat over-sized gas furnace allows me to use thermostat setback - which saves money and is more comfortable.
Just did this, was amazed at how consistent the calc was month to month (once I corrected for non NG consumption). My heating bill conveniently has the heating degree days on it for each billing period.
My furnace is a 70kbtu 90% efficient single stage. Calculation came out to 27-29kbtu depending on assumed balance point. Interesting point of interest is the popular slantfin heat loss calculator gave me a heatloss of around 44kbtu. Looks like it has that 1.4 oversize built into the calcs.
I put a wood stove in last year, it dropped the calculated numbers to around 12kbtu. I run the wood stove from November to March without letting it ever go out.
For the record, there's a typo in this sentence:
"At a balance point of 60°F there are only 40 F° heating degrees, and the implied load is 45 F° x 785 BTU/F-hr = ~31,400 BTU/hr."
Change "45 F°" to "40F°". The product is already correct for "40F°".
Be careful with balance points. There is one figure appropriate for long term average fuel usage calculations and a quite different one appropriate for "how many btu/hr do I need to heat the house at 3am".
For the latter, my *measured* base value is about 1F (= ~700 btu/hr) below the thermostat setting.
Using the example's 785 BTU/F-hr, a 60F base and 70F inside: at 3am, 7850 btu/hr won't be available from electricity use or people and assuming that would cause under-sizing.
Also be careful with "design conditions". You will occasionally see much colder temperatures, sometimes for extended periods.
How would you go about doing these calculations for an all-electric, heat pump system (measured in tons as opposed to BTUs)? Or is that as simple as just using an online converter (ex, https://www.unitconverters.net/power/btu-to-ton.htm) as the last step?
Doesn't this method assume that the house is being held at temp 24hrs/day? Or am I missing something. When I did the calcs, I got a load of 17,566 BTU/hr when dividing the daily amount by 24. When I take into account that the heat is on only in the morning and evening typically, I divide by 9 for a load of 46,843 BTU/hr. My house is about 2,200 sq ft in Portland, Oregon, so the latter seems more reasonable. The furnace is sized at 65,000 BTU/hr.
I also did the calculator that I googled at: https://www.intelligentheatandpower.com/heat-load-from-fuel-use-calculator/ and got an answer of 11,450 BTUh load which also didn't have and input for heating hours/day. I don't believe that at all.
@Dana From reading your comments I assume you have some radiant panels for heat, but I am not clear on what you have for cooling. I too am looking into the SpacePak for hydronic radiant heating, but have been torn on how to deal with cooling, especially given the desire to have a decent ability to deal with latent heat. I have looked at air handlers (2 and 4 pipe), but selection is limited (and overkill), and at both the high velocity systems of which SpacePak makes one. Now I'm thinking that possibly a small ducted mini-split or even ductless one might fit the bill (and If I feel fancy, I could put a desuperheater on it to preheat DHW). My question is really one of wondering what might be throwing you toward the high velocity air system as your pick. I will also add I'm a bit nervous over flip-flopping between heating and cooling in a single buffer tank set-up as we have a pretty large shoulder season where we might heat at night and cool in the day. I've had some folks from Messana wave off such concerns as being frivolous/unwarranted
>"@Dana From reading your comments I assume you have some radiant panels for heat, but I am not clear on what you have for cooling. I too am looking into the SpacePak for hydronic radiant heating, but have been torn on how to deal with cooling, especially given the desire to have a decent ability to deal with latent heat."
The current configuration has a 5 tons of central air (grotesquely oversized for a <<2 ton design load) hooked up to 99 year old uninsulated but otherwise good shape ducts. The room to room balance for both cooling and heating is terrible (made worse by the oversizing) and the upstairs is way underserved no matter what. The duty cycle is way too low for comfort and consistent latent cooling, so in recent years we have used a 1-ton modulating U-shaped Midea window unit (rated CEER 15) placed in the open-loft office at the top of the stairs, which convects well with the kitchen on one side, and the living room on the other. With the doors to rooms open to the common areas or office it keeps up just fine (including latent loads) at the 1% design condition, but doesn't cut it when it's north of 90F.
The heating system is a combination of micro zones, and one large zone covered by the existing air handler, which has a similarly oversized hydro-air coil. During the heating season it could cover the entire house, but with the open-archway living/dining/kitchen/entry the rest of the house gets cold whenever the woodstove in the living room is running. So the rest of the house is micro-zoned for heat.
One zone is entirely plated under-the-subfloor radiant floor designed for 125F AWT, but it doesn't quite keep up since the contractor building that addition (back in the 90s, before I took over) couldn't do arithmetic, and had to add a second layer of 3/4" in order for the finish floor to be level with the rest of the house. To get it that zone to work at 110F AWT we are adding 10-12' of Runtal UF-4 panel-rad in parallel with the radiant floor.
The bedrooms are all micro-zones with cast-iron radiation (master bedroom, first floor bedroom, upstairs bedroom) that all keep up at 125F. The MBR is somewhat marginal even at 125F and going to need ~175 square feet of plated radiant floor to work at 110F. The smaller first floor bedroom works already at 110F but barely, and I'm contemplating adding some suspended tube radiant to give it some margin.
The upstairs bedroom has mostly kneewalls and not a lot of wall area making it a bit awkward (but still possible) to add radiation. But since it's completely underserved by cooling we are considering either at 3/4 ton compact duct cassette in one of three knee-wall attics (they are insulated at the roof deck) and using the compact duct cassette to cover the shortfall when 110F water doesn't keep up. If going with SpacePak the second floor COULD be handled with a small-duct high velocity AC air handler, but the installed price would be insane for the amount of space it would be conditioning (<500 square feet). At more reasonable cost we're considering a small floor mounted slim wall coil in the loft office, and a larger one in the main bedroom area, which would be fine for cooling. With that solution the upstairs bathroom may run cold if the door to the bedroom is closed, but would be fine most of the time, since it has enough cast iron baseboard tucked under & behind the sink & toilet to run just fine most of the time.
In the process of soliciting proposals I have discovered that under the newly adopted energy stretch codes for my city (Worcester MA) the ducts would need to be insulated to the same level as current code for new construction even though they are fully inside conditioned space, most of it in an R15+ insulated wall basement. Given the high insulation retrofitting cost and the amount of head-banging obstruction that would create we are going to demo the duct system entirely and heat the living/dining/kitchen/entry common zone with radiation. The entry, living and dining areas are easily retrofitted with Runtal UF-4 (chosen for the high WAF- I would have been OK with something cheaper) but there is literally no wall area to speak of in the kitchen. The solution there is a combination of a 4' Runtal UF-8 against the small section of wall under the eat-in counter, and ~100 square feet of plated underfloor radiant (Uponor/Wirsbo Joist Trak) under only the exposed floor, not cabinets (so as not to create food spoilage issues inside an overly warm cabinet.)
For cooling with a SpacePak the first floor would have one of those ridiculously expensive high-velocity systems. With the right controls it's possible to get reasonable latent cooling out of it, but during low cooling load times it might get sticky. With a heat pump water heater in the basement a decent chunk of the latent cooling is already in place, but to keep the chilled water plumbing from sweating too much it may need a room dehumidifier as well. Down the road if we ever get around to installing a whole-house ducted ventilation system a whole house dehumidifier could take care of it, though that's a bit like using a 25lb maul to smack down flies in our local climate.
If going with an LG Multi-V the upstairs would get the compact duct cassette, the main zone downstairs would get a 1.5 ton modulating air handler. The main zone currently served by the air handler would then not need new radiation, but the bedrooms (particularly the MBR) would need the upgrades to work the LG's low temp Hydro Kit.
So yeah, it not exactly a cheap HVAC upgrade. But this house is what I've recently heard someone refer to as my "...toe-tag home..." (only moving out in body-bag :-) ). It's unlikely the cost would ever be recouped in a resale, and absolutely NEVER "pay for itself" in energy costs (even at the current USD$0.32/kwh utility price, which is more than twice the lifecycle cost of rooftop PV). But it's hard to place a price on comfort, and the reduction in environmental harm by getting rid of fossil fuels is substantial. The planned rooftop PV would cover only about half the annual use at the house- complicated roof lines and less favorable shading factors get in the way of taking it to Net Zero, but it wouldn't take a huge freestanding array (perhaps on a pergola off the SE corner) could cover that difference, and "worth it" on an NPV basis if current electricity rates persist (or increase.) But I expect electricity prices to dive precipitously after 2030, since by then the cost of utility scale renewables + utility scale storage will be well under the operating cost of the existing regional grids. (See https://www.rethinkx.com/energy )
Question to Dana or anyone else who might know
Is this calculation method from a standard or trade association? Is it officially documented anywhere?
No need to sell me on the merits of using this method. It makes all good sense to me.
I’m trying to pave a repeatable path for myself and others in my Townhouse complex to to follow for replacing their gas furnaces with heat pumps. My current roadblock to getting a right sized heat pump installed is the local municipal government.
They want a CSA F280-12 or HRAI compliant calculation on heat load to provide a permit. Problem is the models predict a much higher heat load than what I actually see looking at gas use. 50% 100% more. Thinking again about what Allision Bailes did with his home, I can’t help but feel chasing model based calculations is a dead end.
https://www.greenbuildingadvisor.com/article/my-undersized-heat-pump-in-an-arctic-blast
Ideally the city would just let me install a small heat pump and suffer the consequences (or reap the rewards). But they believe they hold some liability in approving the permit.
Thanks in advance
This method is not derived from, accepted by or used by any industry standards, but is often used by practitioners in the industry. eg: Borst Engineering, a mechanical contractor in Rogue River Oregon even provides a handy online calculator (among many) on their website:
https://www.borstengineeringconstruction.com/Existing_Building_Energy_Usage_Analysis_Calculator.html
https://www.borstengineeringconstruction.com/Calculators.html
When done appropriately with aggressive numbers ACCA Manual-J will deliver comparable numbers if using ONLY wintertime fuel use, in a IECC climate zone 5 or cooler climate. In zones 4 or lower (sometimes even in zone 5) the heating numbers can be skewed heavily by solar gains houses with a lot of sun-facing window area. I have found significant discrepancies understating the 99% heat load using this method in sunny California zones 3B and 3C, but even there using a 1.4x upsizing factor is usually enough.
The defaults in most Manual-J tools are way too conservative, leading to gross oversizing of heat pumps. The easiest and best freebie Manual-J tool for specifying heat pumps is the BetterBuiltNW tool:
It requires a (free) membership to use it, but it uses much more aggressive default U-factors and air leakage assumptions. It was developed by NEEA consortium member utilities in response to years of complaints from ratepayers participating in their heat pump rebate programs, almost all traceable to severe oversizing. They basically dumbed it down to the point where even HVAC contractors can use it, and being a Manual-J tool recommended by the utility gives a contractor some cover for potential (and almost never real) undersizing problems.
Run a block load with that tool on your own place, see how close it gets to fuel-use derived numbers. In most cases it's within 15%, way better than 50% or 100% using the defaults from some other tools. If that's true in your case, print it out along with the fuel use "sanity check" verification and submit it when applying for the permit- see if they accept it. If need be print out some of their flyers targeted at contractors or utilities (links on the main page), eg:
https://betterbuiltnw.com/assets/uploads/resources/HVAC-ST-Flyer_Contractor_NEEA_FINAL.pdf
If the fuel-measured system is ducted, and the old ducts will NOT be used by the replacement equipment there can also be significant errors. The real-world losses of leaky uninsulated ducts can be hard to estimate, made even worse in air-leaky houses where unbalanced or leaky ducts results in high air-handler driven outdoor air infiltration.
Dana, thanks again for this post as I found it most helpful (cold climate zone 7A) to get a sense of energy use by our home as we look to transition to an ASHP from NG. It makes 100% sense to me with respect to the logic. I also appreciate your comments on ducting as this is something likely often overlooked.
Our calculated actual use of 308 BTU/degree-hour(about 28K BTU at -17 F) is rather dwarfed by the 66K BTU condensing furnace the installer had spec'd.
66K @-17F would be a ENORMOUS load for a townhouse- even an end unit!
I'm curious if you ran a calculation using the BetterBuiltNW tool yet, and how closely it matched the fuel-use derived load number?
@Dana
This article has been immensely useful for my heat load calc. Thank you!
Based on the coldest month gas bill (February), I calculated 25,500 BTU/h for my house at a 3F design temp. That is approx 3,500 BTU/h more than my thermostat runtime-based calculation which gave me 22,000 BTU/h.
I have a question about the following paragraph in your article:
"If the same heating fuel is also used for domestic hot water, this calculation method exaggerates the implied load numbers, since some of that fuel was used by the water heater and sent down the drain. But some of the space heating came via solar gains that would reduce the implied load numbers. These errors tend to balance each other out to a greater or lesser degree."
I use the same heating fuel for my hot water tank and my BBQ. This seems to explain the 3,500 BTU/h difference between the two calculation methods. Aren't solar gains just folded into the overall characteristics of the structure and location, same like number of windows or amount of attic insulation? Or is there a reason why solar gains are special and are offsetting the gas usage by other appliances?
Thanks!
>"Aren't solar gains just folded into the overall characteristics of the structure and location, same like number of windows or amount of attic insulation? Or is there a reason why solar gains are special and are offsetting the gas usage by other appliances?"
Solar gains are special in that they occur during daylight hours. The 99% outside design temperature is almost always at night, when no solar gain is available. Like solar gains, in a Manual-J or IBR methods internal heat gains from people or appliances are not accounted for in the heat load calculation, but very much DO get added in for the cooling load calculation.
In way-better-than-code houses solar gains present a significant error with fuel use load calculation methods. But in very-high performance houses that error hardly matters for sizing heating equipment since even the smallest available heating equipment can oversized for the heat load, and even when undersized temperature undershoots are tiny. But those houses are are the exceptions, not the rule.
This method is not perfect, but does result in equipment sizing that is comfortable & efficient for the vast majority of homes in cool/cold climates, and avoids the grotesque oversizing so common in the industry historically. When replacing equipment it puts a reasonably accurate stake in the ground to work from allowing one to mitigate the worst oversizing errors of the past.
Thanks Dana! I can't say I fully understand , as I thought that fuel use was the grand equalizer of all things but I am just a homeowner, so I trust what you're saying!
Based on my numbers do you think I'll be good with a 2-ton heat pump? I will have backup coils too, just in case.
@dana, toward end of 2022 it sounded like you were leaning Spacepak, but if I followed correctly you did not install them for your lower temp radiant. Am I correct? If so, why did you not move ahead? I’m currently considering for an addition, and to also take advantage of existing panel radiators in the original house we’re adding into. That will only work because the room by room heat loss in existing house is dropping dramatically (going from very leaky and empty 2 by 4 walls to 1 ach50 and lots of cellulose in Larsen trusses) that we will likely get enough heat from them at 110-120 degree supply. Thanks in advance for any insights on Spacepak hydronic option.
This is an excellent write up! While this shouldn't replace a professional assessment, this calculation approach is sure to put you in the right ballpark. I put together a calculator that follows this methodology here: https://www.starlinghome.co/heat-pump-savings-calculator
In the interest in making it easy for folks to calculate, I made some additional simplifying assumptions. For example, instead of finding heating/cooling degree data from the most local weather station, I've applied a state average. This, of course, starts to fall down in large states or states with varying climates. I plan to work on a more advanced version of this calculator to account for this.
Thank you again!
Greetings,
I am just about through my first winter with my new heat pump system. I ended up getting an all-electric Carrier 38MURAQ / 40MUAA 2 ton size. Unfortunately I made a couple of calculation errors in the fuel-based heat load calc. I accidentally multiplied my BTU/F-Hour number by a balance point of 60 instead of 65 for my 2x4 constructed house. I also accidentally used a winter design temp of 3F which came from ASHRAE when I should have used -8F from the Ontario Building Code. Without these errors my design load would have been 29,572 BTU/h and I would have gone for a 2.5 ton unit. It has been a mild winter and my aux heat was only engaged about 4 times for about 30 minutes each, and I'm saving money versus the gas furnace, so no complaints so far. However, I am a bit worried about what happens when (if?) we get a colder winter. The aux heater is 10kW which is actually a 15 kW module with only the 10 kW portion connected.
I wouldn't worry. Using the London, Ontario station for the heating degree days:
2/28/23-2/28/24: 6496 Total, Max 59
2/28/22-2/28/23: 6669 Total, Max 59
2/28/21-2/28/22: 6792 Total, Max 66
So the trailing 365 days have been 4% warmer than the 365 day period starting 2021 and 3% warmer then the next one. That doesn't seem mild in my opinion, just average. If the resistance strips only ran for 2 hours this year, then you're probably still oversized.
Thanks Paul, 4% doesn't seem too much. Oversized though .. you think? My system was working really hard during the coldest days, which were still warmer than the design temp, and aux was definitely needed. Run cycles have generally been 3 to 5 hours at a time on an average winter day. I also had the ducts tested as part of an energy post audit and my static pressure is quite low even though the unit's cfm is maxed out.
I am considering a project where I do further air sealing and insulation (mostly basement rim joist area) and adding a centrally connected ERV. My air change rate is currently 4 at 50 Pa. What do you think? The alternative is basically to do nothing more to this house.
For a variable speed system it can work 24 hours a day and that’s okay. If you’re barely using the strips, you’re meeting the load with just the heat pump. So either right on or oversized.
Good to hear that. It was a mild winter though so it sort of makes sense that I didn't need much aux. Our winter design temp is -22C, but the lowest temp this winter was -15C. The guidance from the government was to size the HP according to the design load so by that definition I would be slightly undersized right? What guideline do you use for sizing a HP?
The nice thing about the way aux worked this winter is that it was only necessary for a short boost in the mornings and then the heat pump carried on for the rest of the day and even all night.
“[Deleted]”
Reply to #56,
"The guidance from the government was to size the HP according to the design load so by that definition I would be slightly undersized right? What guideline do you use for sizing a HP?"
The strips can run for other reasons. Perhaps you were recovering from a setback? That doesn't mean you're undersized.
Right, that's true. I have a 0.5C setback which is small but not nothing. Setbacks are a comfort thing that is usually accounted for in the sizing, right? Or do you consider the "right size" to exclude setbacks and other cases where more heat is required? One thing I noticed is the very low static pressure number. It appears that my ducts were built for more than the 700cfm that my 2-ton system seems to max out at. Would this be more of a duct issue then, than an undersizing of system issue?
No, setbacks aren’t included. This is why I think you’re oversized. If you only used 2 hours of resistance heat (if I recall correctly) then you’re definitely not undersized.
The ducts are probably sized closer to the initial heat loss “calculation”. As you can see, they botched that calculation.
That's interesting... Keep in mind we only got down to -15C whereas the design temp is -22C... my set back of 0.5C seems minor in comparison. Would your expectation be to use aux heat more, and wouldn't that just be more expensive for me?
Our furnace just stopped working. I’m hoping it’s nothing major, but since it’s 23 years old, a replacement might be in the cards. Anyone know how much I might be looking at for a new one? I will be contacting furnace repair in El Dorado https://alphamechanicals.com/service-area/el-dorado-hills-hvac-service/ and really hope they can help us to fix the issue, whatever it is.