Build_ny (we’ll just call him Build) is planning a new house in climate zone 6, and among the quotes he’s received is one from an insulation contractor who’d like to use both open- and closed-cell spray polyurethane foam in both the walls and the roof.
Build says he needs to hit R-25 in the exterior walls, and R-49 in the roof. To get there, the contractor wants to use 1 1/2 in. of closed-cell foam and 4 in. of open-cell foam in the walls, with 3 in. of closed-cell and 7 in. of open-cell foam in the roof.
These two types of polyurethane foam are similar chemically but have different properties. Open-cell foam has lower R-values and allows the transmission of some water vapor. It’s also cheaper. The difference in vapor transmission is an important distinction, and this has Build wondering about the contractor’s proposal.
“I guess I’m worried about creating a dew point in the wall cavity,” Build says in this recent Q&A post. “Could either of these lead to that?”
That’s where we start this Q&A Spotlight.
Beware of declining R-values
The R-value of closed-cell foam declines over time, says Michael Maines, and it would be a mistake not to take that into account. When first installed, closed-cell foam can be rated at about R-7 per inch, he says, but that will fall over time to about R-5.5 per inch (to reach what’s called its aged value). Maines adds that open-cell foam has an R-value of R-3.6 per inch, which should remain constant over time.
“More important is long-term resistance to moisture accumulation, for which you should use the aged values,” Maines says. “Using those values, your walls have about 36% of the total R-value in the impermeable (closed-cell) layer, which…
I understand the need to use closed cell foam in higher numbered climate zones, but in Zone 3, we never use closed cell foam in wood-framed rafters assemblies. Design the house correctly, especially the HVAC system, and use a spray foam professional that understands building science in accordance to the climate zone you are building in and you will have a house that performs. I spend countless hours explaining to clients why solutions they read about in Green Building Advisor that may work in Zone 6 will not work in Zone 3.
Todd Witt
http://www.SynergyHomePerformance.com
Closed cell spray polyurethane foam ranks with XPS as worst among the common insulation choices in terms of global warming potential. Best among the rigid foams is EPS. Mineral wool is similar. Cellulose is among the least damaging to the environment.
I've eliminated the use of ccSPF in my work. With the move towards continuous exterior insulation I am using EPS on roofs. But between rafters and in walls I use cellulose. My designs mostly have unventilated attics and some "cathedral" ceilings. If I were doing ventilated attics then I'd go all cellulose.