![](http://images.greenbuildingadvisor.com/app/uploads/2019/05/20162818/hvac-furnace-air-conditioner-filter-dirty-pleated-media-700x548.jpg)
One of the topics I’ve hammered on for years is the inadequacy of using rules of thumb for sizing air conditioners. The standard one ton of air conditioning capacity for each 400 to 600 square feet of conditioned floor area just doesn’t work. We know that a load calculation based on how a particular house is likely to perform is much better than a rule of thumb. Another area where a rule of thumb dominates is in replacing the filter in your air conditioner (or heat pump or furnace). Change it every thirty days, right?
Is 30 days the answer?
When you buy the standard one inch fiberglass filters for your HVAC system, the instructions on the package usually say to change it every 30 days. This advice gets repeated dutifully by a lot of people and organizations trying to help. And the truth is, you won’t cause any problems by changing your filter every 30 days and you might even prevent some. A few years ago, I spent a day going on service calls with Phil Mutz of Moncrief Heating & Air Conditioning here in Atlanta. As you might expect, some of the problems we found were low air flow due to dirty filters.
Changing the filter every 30 days is a hassle, though. In spring and fall, the filter generally won’t get as dirty because there’s not as much need for heating and cooling, so you can get by with not changing it as frequently. And in a house that doesn’t have much infiltration or duct leakage and a low level of dust overall, the filter can stay clean longer even when being used a lot (unless your return vents are in the floor).
And then there’s the issue of the type of filter. If you’ve been following this blog over the past year, you know I’m a fan of high-MERV filters that are thicker (at least two inches) because they do a much better job of cleaning the air. If you want good indoor air quality (IAQ), you need better filtration and that means a MERV-13 filter. But high-MERV filters also happen to be more expensive so changing them every 30 days is not the so good for your pocketbook.
The good news with high-MERV filters, though, is that they usually hold more dirt. There’s more surface area with thicker, pleated filters so when they capture the same amount of dirt as a standard one inch filter, the air flow rate isn’t affected as much. So how do you know when to change them? Well, if your filter looks like the one in the photo at the top of this article, you’ve waited too long.
How about using the pressure drop across the filter?
I recently wrote about how to get a low pressure drop across a high-MERV filter, and the issue of when to change the filter came up in the comments. Here’s what John Semmelhack wrote there:
“Our general rule is that when the pressure drop across the filter doubles from the initial, clean pressure drop, it’s probably time for a change. With big, deep filters this can take a loooooooong time, and the filters will look absolutely disgusting well before the pressure drop would indicate that it’s time for a change.”
What about the total system pressure?
One thing needs to be pointed out here: Waiting for your pressure drop across the filter to double will work only for a filter that’s designed properly and has a low pressure drop with a clean filter. And you also need a duct system that’s designed properly, without excessive resistance to air flow.
If you put in a MERV-13 filter and the pressure drop across a brand new, clean filter is 0.25 i.w.c., which is not at all uncommon, you can’t let that filter load to the point where the pressure drop is 0.5 i.w.c. That would mean the pressure drop across the dirty filter by itself is equal to what’s allowed for the total external static pressure. That is, the filter has used up all the pressure that’s supposed to be used up in the drops through the whole duct system (and the air conditioner coil in the case of a furnace).
If you want to go to a performance-based method for deciding when to change the filter, you’ve got to make sure your duct system and filter design are appropriate. If they’re not, then you should fix those problems so you can get it to the point where a doubling of the filter pressure drop is your signal to change the filter.
Allison Bailes of Decatur, Georgia, is a speaker, writer, building science consultant, and the author of the Energy Vanguard Blog. You can follow him on Twitter at @EnergyVanguard.