Image Credit: Energy Vanguard
Image Credit: Energy Vanguard The AirCycler central fan integrated supply ventilation system can be coupled with an exhaust-only ventilation system for balanced ventilation.
Image Credit: AirCycler The QuFresh supply-only ventilation system from Air King can be coupled with an an exhaust-only ventilation system for balanced ventilation.
Image Credit: QuFresh
Ventilation is a great thing. Bringing outdoor air into the home and exhausting stale indoor air improves indoor air quality. Well, most of the time, anyway. Sometimes the outdoor air quality is worse than indoor air. Sometimes you bring in too much humidity and start growing mold. And sometimes you bring in the wrong outdoor air. But the issue of outdoor air vs. indoor air is a topic for another article.
Probably the most common type of whole-house mechanical ventilation system in homes is an exhaust-only system. You put some controls on the exhaust fans that are already in the home and those fans are set to exhaust stale air from the home, either continuously or intermittently. The problem is this type of system sucks. Literally. And if your house is sucking from an attached garage, a moldy crawl space, or dirty attic, you could be making things worse.
One way to avoid having a house that sucks is to do balanced ventilation. You exhaust stale air from the house and you supply an equal amount of outdoor air directly rather than relying on the negative pressure of the house to bring in the outdoor air.
Here are five ways to do balanced ventilation. I’ve put them in increasing order of cost, complexity, and efficiency.
1. Open the windows
OK, technically I shouldn’t include this one because it’s not a real solution for most homes. This one works only if the home is in a mild climate that needs to little to no conditioning. But if that’s your situation, you don’t need a fancy ventilation system. Just open the windows.
2. Pair a central-fan integrated supply system with the exhaust fans
A lot of homes get exhaust-only whole-house ventilation (fans plus controls). One easy way to upgrade is to install a central-fan integrated supply system to complement the exhaust-only side. The two most commonly used controls for this are made by AirCycler and Honeywell.
These systems are integrated with the blower in the central heating and cooling system. They bring in outdoor air when the system is running and mix it with the indoor air circulating through the duct system. It gets filtered and conditioned before being introduced into the home. When tied to the exhaust-only controls, you get balanced ventilation.
The main drawback of this system is energy use in systems that don’t have variable-speed blowers. In addition to bringing in fresh air when the system is heating or cooling, it can turn the blower on when the home doesn’t need heating or cooling. And some blowers use a lot of power. Turning on a 400 watt fan to bring in 50 cubic feet per minute of outdoor air is overkill. If you have a high-efficiency heating and cooling system with a variable-speed blower, you should be able to do this at less than 50 watts.
And another drawback is moisture. In a humid climate, running the blower without the compressor on can evaporate moisture on the coil and put it back into the home. (I’ve shown my data on what happens when you leave the fan on continuously in the summer in an article called How Your Thermostat Can Grow Mold and Make You Uncomfortable.) This wouldn’t be quite as bad as that, but it can make things worse. Curt Kinder, an HVAC contractor in Jacksonville, Florida, wrote recently, “Data and experience in my area of operation, northeast Florida, suggest that operating the system fan independently of the compressor raises indoor relative humidity by upwards of 10%.” If that scares you, consider the next three options.
3. Pair a supply fan with the exhaust fans
Another way to get balanced ventilation is to use the exhaust fans with controls and also install a supply fan. You can do this with a bath fan installed to blow air into the home or you can use a fan made specially for this task. I’m thinking of the QuFresh fan made by Air King.
They have two basic models. One has a sensor for temperature and relative humidity, and the other does not. The purpose of the sensor is to limit the amount of ventilation when it’s really cold, really hot, or really humid outside. It’ll still run 15 minutes an hour so you’ll keep getting some ventilation air.
I like the concept and the features in the QuFresh fan. I haven’t had a chance to try one out yet, but they do a lot of good things. You can adjust the flow rate from 30 to 130 cfm. It has a slot for a 2 inch filter that could be up to MERV 13. It’s quiet (0.5 sone at 50 cfm). And it’s relatively inexpensive.
4. Pair a ventilating dehumidifier with the exhaust fans
The strategy here is to use controls on your exhaust fans, as in the previous two, and supply your ventilation air through a whole-house dehumidifier. Many models allow you to do this by providing two intake ports on the dehumidifier, the smaller of which attaches to a duct that goes to the outdoors. We like Ultra-Aire but you can also find good models from AprilAire, Honeywell, and others. (Disclosure: Therma-Stor, which makes Ultra-Aire dehumidifiers, advertises in the Energy Vanguard Blog.)
One drawback of dehumidifiers is the heat they put into your home. The Ultra-Aire model SD12 eliminates that problem by being a split-system dehumidifier. It removes the humidity indoors but puts the heat outdoors. That means it even provides a bit of cooling (about a third of a ton).
5. Use a heat-recovery or energy-recovery ventilator (HRV or ERV)
This is what most people think of when someone mentions balanced ventilation. The photo at the top of the article shows the inside of a typical ERV, with arrows to show the two air streams. (An HRV looks the same but uses a different material in the heat exchanger.)
The operation is simple. It has two fans, one to exhaust stale indoor air, one to bring in fresh outdoor air. It filters both air streams. The two air streams pass through a heat exchanger, a capillary core in most models. The two air streams pass near each other and exchange heat in an HRV and heat and moisture in an ERV. But the two air streams don’t mix.
This is a great way to ventilate a home. It’s also more expensive than the methods mentioned above. Panasonic does have a small “spot” ERV called the Whisper Comfort, but aside from that model, you’re probably looking at $1,000 or more for an ERV or HRV. The biggest difference between this type of balanced ventilation and the previous ones is the heat exchanger. You get balanced ventilation with recovery, which means you don’t need to do as much conditioning of the outdoor air you bring in.
Finding balance
There’s your quick rundown of the main ways to do balanced ventilation. We’re seeing a lot of creativity in the ventilation market these days because ventilation is a big deal. I think we’ve gotten to the point where we rarely have to fight the battle about the need for airtight houses. The old myth that a house needs to breathe, while not completely gone, has mostly been relegated to the dustbin of bad thinking.
But let’s be clear about what balanced ventilation really means. It doesn’t mean the building is always at neutral pressure with respect to outdoors. Wind, stack effect, and other mechanical systems can always unbalance a building. When we talk about a balanced ventilation system, we mean simply that that particular system doesn’t result in the building going positive or negative because it’s exhausting and supplying equal amounts of air.
Another point here is that my main motivation in writing this article was to show some ways you can convert an exhaust-only system to a balanced system. Methods 2 and 3 above show how you can do that relatively easily and inexpensively. Method 4 would be a good way to do it in the humid climates of the southeastern US.
And one more thing. I was going to make this a list of six ways to do balanced ventilation but decided to save the other one for a separate article. Going a step beyond the ERV, you could go with a souped-up ERV. There are two companies making devices that include balanced ventilation with recovery, a small heat pump, better filtration, and more. One is the Conditioning ERV, or CERV, by Build Equinox. The other is the Minotair by Minotair Ventilation. We’ve got two HVAC design jobs going right now that will be using these devices, so stay tuned for more on these later.
Meanwhile, try to stay in balance. Or at least be positive.
Allison Bailes of Decatur, Georgia, is a speaker, writer, building science consultant, and the author of the Energy Vanguard Blog. You can follow him on Twitter at @EnergyVanguard.
14 Comments
small house ventilation
Allison: Thank you for the article on balanced ventilation. Since we are building tighter homes, I am sure this issue will come up again many times.
I do have an issue that you might help me with. I volunteer with the city of Bozeman and its Community Affordable Housing Advisory Board. We are collaborating with MSU's architecture department and some local non profits to build some very small, affordable, transitional housing.
Here's where you come in: These homes are about 170 square feet with a 1 ACH or less. I just finished a house that tested .35 ACH at completion. You can imagine with one person living, showering, cooking in a very small unit that is so tight there are virtually no air exchanges, there are going to be moisture issues. I asked the architecture students where they think all of the moisture is going with only one bath fan. We should consider that the tenant may turn off that fan. A couple of them speculated, correctly, that the moisture would end up in the walls.
Do you have a low cost solution? How much moisture do we need to remove? Will a Panasonic fan/ERV solve the problem or do they need a more elaborate solution? Opening the windows when it is zero outside probably will not cut it.
Let me know if you have any ideas?
Response to Anders Lewendal
Anders,
An exhaust-only system using a high-quality bathroom exhaust fan like the Panasonic will work. Of course, the homeowners have to use the fan properly. If the fan is disabled or turned off, it clearly won't work.
The other option is a pair of Lunos fans.
-- Martin Holladay
Question for Martin
What about the TwinFresh? (I'm not familiar with this products.) It makes a single room ERV and HRV. Both units are low-cost and good to -4 degrees.
Panasonic Whisper ERV family
IMO, for high-performing houses there is no other choice than ERV/HRVs. Panasonic ERVs are very affordable with wide range outputs, from 40/20 cfm for small houses, to 80-150 cfm ranges for mid and large homes, and the best part is that all are between $250-$500 plus install. Broan has some fairly affordable units too in the mid-rage size.
Response to Steve Knapp (Comment #3)
Steve,
I have no direct experience with the TwinFresh products. I agree with you that the prices are low.
-- Martin Holladay
Lunos
In addition to the Twinfresh and Panasonic Whispercomfort, the Lunos (http://www.lunoscanada.com/lunos-e%C2%B2.html) also has an in-wall solution for HRV functionality. The Lunos units are paired to create a ventilation system. It seems like a great idea, though perhaps not a cost savings (depending on what the ductwork costs.). To echo Anders' question above, I don't see how an HRV can take care of humidity. Minotair has an interesting ERV+dehumidificatino system (https://www.minotair.com/home_en/) but again we are getting into higher cost and higher complexity. I also worry about the fabled toaster+coffeemaker problem (or DVD+TV) problem, which ties two separate systems together making it impossible to upgrade just one, and rendering the system useless if 1/2 breaks.
IMO, there there should be
IMO, there there should be more emphasis on "pressure managed" ventilation (vs balanced ventilation). There is potential to improve things, not just leave them unchanged.
Also note that a HRV can easily cause unbalanced or non-pressure-neutral ventilation. For example, when sharing ducts with an intermittent furnace. Or a supply duct in a room with no return duct.
More info on VENTS-US HRV
I was able to track down the VENTS-US single room HRV at an orange big box store for about $450. Interestingly, it is listed under Hydroponic Gardening - Grow Room Ventilation. Perhaps this has to do with UL listing (just speculating here). It is intersting to compare the VENTS-US website documentation of the TwinFresh Comfo RA1-50-2 with its USA marketing as a grow room ventilator.
CERV/Minotair pricing
Again, back to my toaster+coffeemaker analogy, is there any cost savings to combining conditioning with an ERV system? Or is the impetus to do so enhanced functionality? Could combining these systems be detrimental by creating enhanced complexity and be prone to system failure? The thought of it kind of makes me long for Option 1 (opening some windows).
If all you need to deliver is
If all you need to deliver is ventilation air and dehumidification, then combining ducts can be a significant cost savings.
what's wrong with...
What's wrong with a simple (through wall?) ERV or HRV and a stand alone dehumidifier like we used to run in the old days. Seems to me the less ductwork the better.
I think I'm talking to myself here...
But what I find now is that when I factor in all the duct-work, the cost of installing multiple systems, etc, the Minotair is looking more and more interesting for a ~1800SF home, since it should be able to accomplish all the heating, cooling, and dehumidification with little need for the $500 supplemental heater (which I will probably install just for safety). I also have begun to loathe the idea of a split system whirring next to my house, but this has to do with the design and the lack of any "dead" facades which would not be impacted by the outdoor unit.
Ethan
" the lack any 'dead' facades which would not be impacted..."
Well done. I hate going to see a new house and finding a throw-away facade you just walk by to get to something nice.
worse is...
A nice home with 2 or 3 mini split condensers stuck to the side that the designer forgot to plan for. I think it is important to consider the visual impact of mechanical systems since we think of the visual impact of most other parts of the house. Imagine if cars were really cool looking except they had the engine bolted onto the hood.