![](http://images.greenbuildingadvisor.com/app/uploads/2021/09/03070107/Vented-attic-Fine-Homebuilding-2-700x369.jpg)
There are several reasons why builders have so many roof-venting questions. For one thing, building codes concerning roof venting are confusing. For another, builders are often uncertain about when unvented roofs are acceptable. If they are carefully detailed, either vented or unvented roofs perform well—but whether vented or unvented, poorly detailed roofs can fail quickly, especially in a cold climate.
Why do we vent roofs?
Builders include a ventilation channel under roof sheathing in hopes that moving ventilation air will remove moisture that has escaped from the house through air leaks in the ceiling. In some climates, we include a ventilation channel under roof sheathing in hopes of reducing the frequency of ice dams.
According to building scientists, roof ventilation is less effective at drying roof sheathing or reducing ice dams than commonly thought. Moreover, some building codes imply that indoor air travels to roof sheathing via vapor diffusion. (These codes are a legacy of an earlier era—the benighted era when vapor barriers were mistakenly seen as the best solution to moisture problems.) In fact, vapor diffusion has very little to do with the types of moisture transport that affects roof sheathing. In most homes with damp roof sheathing, the moisture reaches the roof sheathing via air leaks from the interior, not via vapor diffusion, so the presence of a vapor retarder or vapor barrier near the insulation is far less important than the presence of an air barrier.
If you are concerned about keeping roof sheathing dry or reducing ice dams, make sure that your house has an airtight ceiling, and verify your air-sealing techniques by performing a blower-door test. For dry roof sheathing, an airtight ceiling is more important than the effectiveness of your vent channel.
For more information on roof-venting effectiveness, see “All About Attic…
27 Comments
Martin - great post - as usual - however, "If you are building an unvented cathedral ceiling or an unvented attic, and you are installing air-impermeable insulation only" and I use standing seam metal roof - do or don't I - need to provide an air space (slats or 2x4) between the roof underlayment panels and the metal. I have read and read - and still not certain, seems some do some don't. I have basically a 6/12 shed roof - will be fully sealed envelope. Thanks RB
Russell,
The answer to your question depends on the type of standing-seam roofing you will be installing. Contact the roofing manufacturer or the roofing installer to determine the exact requirements of the manufacturer and installer.
If widely read this blog would forestall about half the posts on GBA's Q&A section.
Thanks, Martin! I have a question about spray foam being in direct contact with the underside of the sheathing in an unvented attic. In a previous discussion about insulating unsheathed walls in old homes, it was mentioned that foam board can be put against the lap siding and then insulated behind, with the space between the foam board and the lap siding acting as an air gap. Curious, does the same apply to roof insulation? For example, if the home has slats underneath the sheathing (left over from old cedar roofing), would it still be better to spray foam directly against the slats and the sheathing, or would it be better to line space between the joists with asphalt paper and then spray foam, leaving the air gap between each slat in place?
Jasiu,
There is no definitive answer to your question, but my advice would be to include the asphalt felt layer. The reason is that closed-cell spray foam glues everything together, and closed-cell foam is hard to remove. If you ever have sheathing rot in 20 years, the roofer who makes repairs will be grateful if you include the asphalt felt, or will curse your name if you don't.
Thanks so much, Martin! That was my plan, so just wanted to double check I wasn't overlooking something. Really appreciate it, as always!
Martin,
I have a historic home in Redlands California that needs re-roofed. It is a 2-story home with a floored, unfinished attic. It currently has 1 x 4 skip sheathing with wood cedar shingles and no insulation at all. I was hoping to finish the attic into a living space, but leave the open rafter appearance (1 x 4 and wood shingles) from inside the attic space. Therefore, any insulation and venting (if necessary) would be done from the outside. Possibly considering an unvented cathedral assembly. Was planning to use rigid insulation and a metal standing seam roof.
Need to make sure this is done right. Do you know of a consultant that can help me design it correctly; or perhaps a GBA contact.
Thanks Martin.
Rick in Redlands
Rick,
GBA has a "Green Building Bulletin Board" with a list of green building consultants. The most likely one for you to call is Ann Edminster of Pacifica, Ca. Her contact info:
Ann Edminster
Design Avenues
115 Angelita Ave.
Pacifica, CA 94044
650-355-9150
If she can't help you, she may be able to suggest someone who can.
Martin,
Thank you very much, I have been looking for someone for quite awhile.
Will give her a call.
Rick in Redlands
I'm building a pole barn house with a metal roof on purlins and no sheeting. The attic will be insulated with cellulose loose fill. It is wildland fire prone and very windy when it rains here. The climate zone is 6. I'd like to avoid vents. Maybe just vented foam closure at the ridge. It seems like without wood sheeting the metal should be able to bake mousture out of the attic and through just a vented ridge? And there is less worry of rotting wood.
Thanks
Jim,
I'm not a fan of metal roofs over purlins without sheathing, unless you're talking about a barn or an equipment shed, because under some weather conditions, you'll get condensation on the underside of the metal roofing, and this condensation will drip on the insulation below. Usually, this moisture evaporates before you get a ceiling leak, but in general, an insulated house deserves roof sheathing.
As long as you install an airtight ceiling, and the house is tested with a blower door to make sure that your ceiling really is airtight, you don't have to worry too much about attic venting. If you have wildfire risks, you should skip the soffit vents.
For more information, see "Insulating a Pole Barn."
Hi Martin, thanks for the fast reply,
Trusses are already ordered for 4ft on center and this roof assembly was chosen due to the high sheathing costs.
The ceiling will be tongue and groove that can span the 4 ft spacing. And a poly vapor barrier above the T&G. Considering having poly vapor barrier behind the drywall exterior walls as well. As this insulation is mostly only for heating days and very few cooling days.
Our insulation supplier has vinyl faced fiberglass that comes in an unrated R value thickness of about 1in that is used specifically for condensation under metal roofs. Not sure if you think this is a useful product? It would also dampen any roof noise. Or I have seen projects where people put synthetic roofing underlayment directly on purlins
Thanks
Jim
Jim,
This is a big topic. The basic story is that you have chosen a construction system developed for agricultural buildings, and you are trying to use the same system for a residence -- and that may lead to problems.
For more information, see "Insulating a Metal Building." (I know that you aren't planning to build a metal building, but there are issues with metal buildings that also apply to pole barns.)
The short answer is that vinyl-faced fiberglass insulation installed between your metal roofing and your purlins will reduce condensation problems. Make sure that your roofer is on board with your plan before you order the insulation, though.
Martin, I have been reading for days about the newest insulated wall and roof assemblies, and I am completely overwhelmed.
The building will be a large shop/residence in Zone 6 - stick built (2” x 6”s), 30’ x 80’ with 12’ walls, slab on grade. Roof system will be 30’ wide-spread trusses, ~8’ high on 2’ centers (snow loads 100lbs and wind 115 mph gusts) with 7.25” high energy heals and a 12’ “box” space for storage running the length of the roof space between the webs. Exterior for roof and walls will be 24 gauge 7/8s corrugated black metal, run vertically. No overhangs, no soffits, no extended gables. Minimal and modern.
What would be a couple of workable structures for the walls and the roof? Can I use one structure for both? I would like to stay away from thick layers of exterior foam that would require significant windows and door extension work. I was thinking about ZIP r6 applied directly to the studs on the exterior (although delivery time will be many weeks), followed by 2” of closed cell foam (sprayed or cut and cobbled) in the interior cavity, with bat insulation filling the rest of the cavity, thus achieving the 20r 5r+ recommendation. No vapor barrier after the studs. The only difference between the wall and roof structure would be ice and water shield applied to the ZIP r6 on the roof (assuming that I can use ZIP r6 on the roof, and even after speaking with Huber engineering, I can’t determine whether that would be permissible – and if I can’t use ZIP r6, I suppose I would use ZIP brown with no insulation, but then I don’t know what insulation to install, where to install it, or how much to install.)
I can’t determine whether the above meets the 35% ratio requirement, whether cut and cobble closed cell foam in the cavity would be treated as “exterior” R for the purposes of the ratio, whether a condensation plane will result in some place where it shouldn’t be, whether I would need a rain screen even though the vertical corrugated will self drain, etc.
Is there some source that presents a limited, practical number of options and simply provides a few examples with associated pros and cons of each rather than presenting a maze of technical analyses and extended discussions and arguments on issues I cannot comprehend? What would you recommend? Thanks so much.
Ljung,
Your question ("What would be a couple of workable structures for the walls and the roof?") is confusing, because I don't think you have a structural question. (Your structure is your studs and roof trusses, supplemented by sheathing.) I think you're asking about insulation, not structure.
The cut-and-cobble approach shouldn't be used for unvented roofs. Cut-and-cobble is a very labor-intensive approach that is never used by insulation contractors. More information here: "Cut and Cobble Insulation."
As far as I know, Zip-R sheathing can't be used for roofs--only for walls.
Don't be tempted to leave out the sheathing. For more information on this topic, see "Insulating a Pole Barn."
Unless the 12-foot "box storage" area in your attic needs to be inside conditioned space, your ceiling insulation should follow your horizontal ceiling rather than following the roof slope.
If you want to use a continuous layer of rigid foam on the exterior of your walls, go for it. I recommend using reclaimed (recycled) rigid foam for environmental and budget reasons. Then fill your studs with whatever fluffy insulation you prefer. For more information, see "Calculating the Minimum Thickness of Rigid Foam Sheathing."
You're right. I didn't mean the "structure" but rather the "assembly" which would include the structure and the insulation (and the insulation design depends upon the structure). The "box" must be conditioned, so I planned to wrap all of the sheathing from wall to roof with WRB, with the roof insulation following the truss line. I don't think I can use Zip r on the roof. So if I used foam on the roof in conjunction with standard brown Zip, would I apply the foam to the trusses first, followed by brown Zip, followed by ice and water shield, and then attach the corrugated through the Zip, through the foam, and into the truss members? If the Zip is applied first followed by foam, will I have to use nailers on the foam or can I attach the corrugated directly through the foam and into the truss members? Am I correct in assuming that with vertically oriented corrugated, I would not need a rain screen? Thanks for your advice!
Ljung,
Here's an article with the information you need: "How to Install Rigid Foam on Top of Roof Sheathing."
I should have mentioned roof overhangs in my previous response. Here's my opinion: if it's not too late, rethink your decision on roof overhangs. More information here: "Every House Needs Roof Overhangs."
Martin: Of course, you are correct re overhangs. I lived in Switzerland for 12 years - out in the mountains - so I smiled with recognition at the picture in your article. I'm afraid this is one of those times where architectural style trumps best practice! See the pictures attached. Our building will be similar in style but with a 6/12 pitch. That building will match two small shed-roof cabins of similar style here in Montana sheep country. All will have Swiss/German sturmrouladen (rolling storm shutters). Do you offer consulting services?
Ljung,
No, I don't offer consulting services. I'm a journalist, not a consultant. Fortunately, you're in luck: advice provided on this web site's Q&A pages is free. If you want to post a question, here is the link: GBA's Q&A page.
Hi Martin. I haven't seen anything written about how to insulate a partial cathedral ceiling. In the section below, the diagonal hatching is vaulted. As you can see, the rafters continue up to a central ridge line. The plan is to do a vented attic with cellulose or rockwool in the rest of the ceiling, and closed cell foam in the vaulted section. Will this work? How should the two types of insulation intersect? This is a remodel, so foam above the roof sheathing isn't an option. Thank you in advance..
Johanna,
Your plan should work, with a couple of caveats:
1. Make sure that your soffit vents (on the side of the roof that connects to the vented attic) meet code requirements for net free area for your vented attic. You will have fewer linear feet of soffit vent than usual, because one side of your attic has soffits that will be blocked by spray foam.
2. Think through how you will insulate the side of the cathedral ceiling that faces the vented attic. Spray foam will probably work better there than cellulose insulation, because cellulose insulation might slump.
Thank you Martin. One more issue and another drawing. I want to do an adjacent, smaller gable as a conditioned attic space for storage. My plan is to do spray foam at the roof deck and build an insulated wall between the two spaces, with an insulated door between them. Do you see any issues? Thanks again.
No issues.
I am planning a low slope unvented roof insulated to R~42 in Quebec. When using a combination of closed cell spray foam (R~29) on the underside of the roof sheathing and roxul between the rafters do I need to use the 2/3 1/3 rule?
Also planning on a vapour permeable roofing membrane.
Thanks
User 7232928,
While Malcolm Taylor referred you (in Comment #25, below) to Assembly #4 in my article ("Five Cathedral Ceilings That Work"), I think he actually meant to refer you to Assembly #5. The type of assembly you are talking about is a flash-and-batt assembly.
Depending on your location in Quebec (which can range, I believe, from DOE Zone 6 to DOE Zone 8), the spray foam layer should represent between 51% of the R-value of the total assembly (in Zone 6) to 71% of the R-value of the total assembly (in Zone 8). So you'll need between R-22 and R-30 of spray foam, with the balance of the total (assumed to be R-42) provided by the mineral wool batts.
Thanks Martin. I'll edit my post.
User...928,
See roof assembly #5 in this link: